Question

In: Electrical Engineering

4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...

4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows:

RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ.

The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit.

Problem 4.12 For the transformer in problem (4.11), determine the efficiency when operating with, 1. rated current, rated voltage and lagging power factor of 0.8, 2. 80% of rated current, rated voltage, and unity power factor. Problem

4.13 Calculate the voltage regulation of the transformer in problem (4.11) when delivering,

1. rated current at 0.9 lagging power factor,

2. rated current at unity power factor, and

Solutions

Expert Solution


Related Solutions

A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
A 60-Hz, 208-V, 2 pole wye connected induction motor is rated at 15hp. The equivalent parameters...
A 60-Hz, 208-V, 2 pole wye connected induction motor is rated at 15hp. The equivalent parameters are as follows: RS = 0.2 Ω RR’ = 0.120 Ω XS = XR’ = 0.41 Ω Xm = 15 Ω The machine has negligible miscellaneous losses but experiences mechanical loss and core loss of 250 W and 180 W, respectively. For a slip of 5 %, determine a) The line current. (44.8  -25.5  A) b) The stator copper losses (1.205 kW)...
A 1.5 KVA, 220/120 V, 60Hz real step-down transformer has the following parameters that are all...
A 1.5 KVA, 220/120 V, 60Hz real step-down transformer has the following parameters that are all referred to the primary-side: the total copper loss R = 2.4 Ω, the core loss Rc = 2.4 KΩ, the magnetization reactance Xm = 2 KΩ, and all the leakages are negligible. Suppose that the output port in the secondary-side is operated at full-load and rated voltage with the unity power factor p.f. = 1. (a) Find the power factor p.f.1 at the primary-side...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is adjustable from no load to 120 percent rated KVA. The percent resistance, percent reactance, and percent core loss are m+1.56, m+3.16, and m+0.42 respectively. For 2 KVA increments of load, tabulate and plot the efficiency of the transformer from no load to 120 percent rated load. Use Matlab n=20 m=.2
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of...
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of 0.56 , 33 and 5.57 respectively. For 10 degree increments of power-factor angle, tabulate and plot percent regulation, and efficiency. Power factor for operation between 0.5 lagging and 0.5 leading.
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor. No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW Stator resistance between line terminals = 2.34 Ω. Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
A 2400-W oven is connected to a 240-V source. 1. What is the resistance of the...
A 2400-W oven is connected to a 240-V source. 1. What is the resistance of the oven? Express your answer to two significant figures and include the appropriate units. 2. How long will it take to bring 110 mL of 25 ∘C water to 100∘C assuming 65 % efficiency? The specific heat capacity of water is 4186 J/(kg⋅∘C). Express your answer using two significant figures. 3. How much will this cost at 12 cents/kWh? Express your answer using two significant...
Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with...
Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with a 50-Hz, 50-kVA, star-star transformer bank of vector group Yy0. Both have a bank ratio of 2000/200-V. The equivalent impedances referred to the respective secondaries are ZΔ = 0.1106/60.2° Ω and ZY = 0.0369/60.2° Ω. (a) Assuming the load switch to be open, draw the connection diagram   (3.0 marks). (b) Determine the magnitude of the current circulating in each transformer secondary   (15.0 marks). (c)...