A single-phase 300-kVA, 220/4400 V, 60 Hz transformer yielded the following information when tested: High voltage...

A single-phase 300-kVA, 220/4400 V, 60 Hz transformer yielded the following information when tested: High voltage winding open: Voltage=220 V, Current=40 A Power=l 000W Low voltage terminal shorted: Voltage= 195 V, Current=68.18A Power=4000W Find the equivalent circuit of the transformer as viewed from the high voltage Calculate the .efficiency of the transformer when it delivers its rated load at rated terminal voltage and 8 power factor lagging.

Solutions

Expert Solution

Open circuit test gives (i) the core loss at rated voltage and frequency (ii) the shunt branch parameters of the equivalent circuit and (iii) turns ratio of the transformer.

Short circuit test gives (i) ohmic loss at rated current and frequency and (ii) the equivalent resistance and equivalent leakage reactance.


Related Solutions

A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage side: ?? = 57.6??, ?? = 16.34??, ??? = 2.784? and ??? = 3.5?. If a load of ????? = 16∠30°? connected to the low-voltage side: a) Find the voltage regulation? b) Draw the phasor diagram? c) Find the efficiency of the transformer? d) Repeat part a and b at ????? = 16∠ − 30°??
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows: RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ. The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit. Problem...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor. No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW Stator resistance between line terminals = 2.34 Ω. Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage...
The secondary of a 500kVA, 4400/500 V, 50Hz, single-phase transformer has 500 turns. A) determine emf...
The secondary of a 500kVA, 4400/500 V, 50Hz, single-phase transformer has 500 turns. A) determine emf per unit. B) primary turns. C) secondary full load current D) maximum flux E) gross cross-sectional area of the core for flux density of 1.2 tesla F) if the core is square cross-section find the width of the limb
A 1.5 KVA, 220/120 V, 60Hz real step-down transformer has the following parameters that are all...
A 1.5 KVA, 220/120 V, 60Hz real step-down transformer has the following parameters that are all referred to the primary-side: the total copper loss R = 2.4 Ω, the core loss Rc = 2.4 KΩ, the magnetization reactance Xm = 2 KΩ, and all the leakages are negligible. Suppose that the output port in the secondary-side is operated at full-load and rated voltage with the unity power factor p.f. = 1. (a) Find the power factor p.f.1 at the primary-side...
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100...
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100 kVA with Zeq = 0.5 + j0.8 Ohm. If an autotransformer is built from this conventional transformer to supply a load at 2640V with supply voltage 2400V. Draw the autotransformer and calculate Zeq, the voltage, current and apparent power rating of the auto transformer. Also calculate the apparent power rating advantage of autotransformer over conventional transformer.
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following parameter values in Ω/phase referred to the stator: R1 = 0.3 Ω. R2' = 0.15 Ω X1 = 0.5 Ω. X2'= 0.21 Ω Xm = 13.25 Ω The total rotational losses are 450 W. The core loss is lumped in with the rotational losses. For a slip of 0.02, and based on approximate equivalent circuit, determine: (i) The rotor speed. (ii) The stator current....
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT