Question

In: Electrical Engineering

The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...

The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor

Solutions

Expert Solution


Related Solutions

A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is adjustable from no load to 120 percent rated KVA. The percent resistance, percent reactance, and percent core loss are m+1.56, m+3.16, and m+0.42 respectively. For 2 KVA increments of load, tabulate and plot the efficiency of the transformer from no load to 120 percent rated load. Use Matlab n=20 m=.2
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100...
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100 kVA with Zeq = 0.5 + j0.8 Ohm. If an autotransformer is built from this conventional transformer to supply a load at 2640V with supply voltage 2400V. Draw the autotransformer and calculate Zeq, the voltage, current and apparent power rating of the auto transformer. Also calculate the apparent power rating advantage of autotransformer over conventional transformer.
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows: RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ. The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit. Problem...
Exercises 1. A 25 kVA single-phase transformer has the primary and secondary number of turns of...
Exercises 1. A 25 kVA single-phase transformer has the primary and secondary number of turns of 200 and 400, respectively. The transformer is connected to a 220 V, 50 Hz source. Calculate the (i) turns ratio, and (ii) mutual flux in the core. 2. A 25 kVA, 2200/220 V, 50 Hz single-phase transformer’s low voltage side is short-circuited and the test data recorded from the high voltage side are P=150 W, I1 = 5A and V1 = 40 V. Determine...
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of...
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of 0.56 , 33 and 5.57 respectively. For 10 degree increments of power-factor angle, tabulate and plot percent regulation, and efficiency. Power factor for operation between 0.5 lagging and 0.5 leading.
Derive the expressions of the average load voltage and current in single-phase full-wave controlled rectifier (bridge...
Derive the expressions of the average load voltage and current in single-phase full-wave controlled rectifier (bridge rectifier) and resistive load. Draw the waveforms of supply voltage, output voltage, output current and thyristor current.    In a single-phase full-wave controlled rectifier (bridge rectifier) and resistive load, it is desired to get an average load voltage of 50 V. Determine the firing angle if the ac supply voltage is 150 V. If the average load power is 300W, calculate the average load...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor. No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW Stator resistance between line terminals = 2.34 Ω. Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage...
A 6-pole, 50 Hz, 3-phase induction motor running on full load develops a useful torque of...
A 6-pole, 50 Hz, 3-phase induction motor running on full load develops a useful torque of 160 Nm when the rotor emf makes 120 complete cycles per minute. The windage and friction loss is 1005.30 Watt. It is assumed; the core loss is lumped together with the windage and friction loss. The total stator loss is given to be 800 Watt. Compute: a) Shaft power output, b) The copper loss in the rotor winding,c) The input power to the motor, and d) The...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage side: ?? = 57.6??, ?? = 16.34??, ??? = 2.784? and ??? = 3.5?. If a load of ????? = 16∠30°? connected to the low-voltage side: a) Find the voltage regulation? b) Draw the phasor diagram? c) Find the efficiency of the transformer? d) Repeat part a and b at ????? = 16∠ − 30°??
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT