Question

In: Electrical Engineering

2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is...

2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is adjustable from no load to 120 percent rated KVA. The percent resistance, percent reactance, and percent core loss are m+1.56, m+3.16, and m+0.42 respectively. For 2 KVA increments of load, tabulate and plot the efficiency of the transformer from no load to 120 percent rated load. Use Matlab

n=20

m=.2

Solutions

Expert Solution

clc
close all
clear all

n = 20;

m = 0.2;

full_load_va = (400 + n)*1000;

primary_voltage = 2300 + n;

secondary_voltage = 230 + n;

pu_resistance = (m + 1.56)/100;

pu_reactance = (m + 3.16)/100;

frequency = 60;

pu_core_loss = (m + 0.42)/100;

power_factor = 0.8;

full_load_power = full_load_va*power_factor;

full_load_var = full_load_va*(sqrt(1 - (power_factor)^2));

base_VA = full_load_va;

base_voltage = primary_voltage;

base_current = base_VA/base_voltage;

actual_resistance = pu_resistance * ((base_voltage)^2)/base_VA;

actual_reactance = pu_reactance * ((base_voltage)^2)/base_VA;

actual_core_loss = pu_core_loss * full_load_power;

maximum_VA = 1.2*full_load_va;

load_VA = 0:2000:maximum_VA;
% efficiency = [];
% efficiency(1) = 0

for i = 1:length(load_VA)
  
primary_current(i) = load_VA(i)/primary_voltage;

efficiency(i) = (load_VA(i)* power_factor) / ((load_VA(i)* power_factor)+ actual_core_loss + ((primary_current(i))^2*actual_resistance))*100;

end

figure(1)
plot((load_VA/1000), efficiency)

title('Efficiency vs Load')
xlabel('No Load KVA <= KVA <= Maximum KVA')
ylabel('Efficiency')
grid on

Efficiency vs Load 100 90 80 70 Efficiency 60 50 40 30 20 10 0 600 100 200 300 400 500 No Load KVA <= KVA <= Maximum KVA

Efficiency vs Load 98 96 94 Efficiency 92 90 88 86 50 500 100 150 200 250 300 350 400 450 No Load KVA <= KVA <= Maximum KVA


Related Solutions

The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
1) A 25 kVA transformer supplies a load of 12 kW at power factor of 0.6...
1) A 25 kVA transformer supplies a load of 12 kW at power factor of 0.6 lagging. How much kVA can be added before the transformer is at rated load a)when the added load is at 1.0 pf? b)when the added load is at 0.866 pf leading?
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of...
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of 0.56 , 33 and 5.57 respectively. For 10 degree increments of power-factor angle, tabulate and plot percent regulation, and efficiency. Power factor for operation between 0.5 lagging and 0.5 leading.
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows: RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ. The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit. Problem...
Q1. A station supplies 250 kVA at a lagging power factor (p.f) of 0·8. A synchronous...
Q1. A station supplies 250 kVA at a lagging power factor (p.f) of 0·8. A synchronous motor is connected in parallel with the load. If the combined load is 250 kW with a lagging p.f. of 0.9, determine : (i) the leading kVAR taken by the motor. (ii) kVA rating of the motor. (iii) p.f. at which the motor operates. Q2. A factory consists of the following (i) An induction motor of 150 h.p with 0.7 p.f lagging and 80%...
Table 1 Load Rating Power Factor Lighting 41.1kW 0.7 Lagging Lights 12.2 kVa 0.67 Lagging Ventilation...
Table 1 Load Rating Power Factor Lighting 41.1kW 0.7 Lagging Lights 12.2 kVa 0.67 Lagging Ventilation fans 9 kVa 0.7 lagging Heat pump 18 kW 0.707 Lagging misc equipment 11.3 kVa 0.55 lagging peak charging demand 209 kW unity Calculate the following for the car park using the data from Table 1: a) the maximum real power demand P (kW) b) maximum reactive power demand Q (kVAr) c) the total apparent power demand S (kVA) d) also, calculate the maximum...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor. No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW Stator resistance between line terminals = 2.34 Ω. Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage...
A three-phase positive sequence Y-connected source supplies 12 kVA with a power factor of 0.75 lagging...
A three-phase positive sequence Y-connected source supplies 12 kVA with a power factor of 0.75 lagging to a parallel combination of a Y-connected load and a Δ-connected load. The Y-connected load uses 6 kVA at a power factor of 0.6 lagging and has an a-phase current of 12∠−30∘A Part A: Find the complex power per phase of the  Δ-connected load. (VA) Part B: Find the magnitude of the voltage. (Volts)
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
A single-phase 300-kVA, 220/4400 V, 60 Hz transformer yielded the following information when tested: High voltage...
A single-phase 300-kVA, 220/4400 V, 60 Hz transformer yielded the following information when tested: High voltage winding open: Voltage=220 V, Current=40 A Power=l 000W Low voltage terminal shorted: Voltage= 195 V, Current=68.18A Power=4000W Find the equivalent circuit of the transformer as viewed from the high voltage Calculate the .efficiency of the transformer when it delivers its rated load at rated terminal voltage and 8 power factor lagging.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT