Question

In: Electrical Engineering

A 1.5 KVA, 220/120 V, 60Hz real step-down transformer has the following parameters that are all...

A 1.5 KVA, 220/120 V, 60Hz real step-down transformer has the following parameters that are all referred to the primary-side: the total copper loss R = 2.4 Ω, the core loss Rc = 2.4 KΩ, the magnetization reactance Xm = 2 KΩ, and all the leakages are negligible. Suppose that the output port in the secondary-side is operated at full-load and rated voltage with the unity power factor p.f. = 1.

(a) Find the power factor p.f.1 at the primary-side input port;

(b) What is the voltage regulation (V R)?

(c) Determine the power efficiency η .

Solutions

Expert Solution


Related Solutions

4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows: RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ. The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit. Problem...
In a step-down converter, Vd = 25V, Vo = 15 V, Io = 1.5 A, Ls...
In a step-down converter, Vd = 25V, Vo = 15 V, Io = 1.5 A, Ls = 200 µH, C = 500µF, and fs=50 kHz. (a) Plot the iL and υL for a period of Ts showing clearly the values of iLpeak, and υL. Assume boundary operation.
What is difference between a 120V/240V step-up and 240/120 V step-down single phase transformers? Both transformers...
What is difference between a 120V/240V step-up and 240/120 V step-down single phase transformers? Both transformers are rated 5 kVA and operated at 60 Hz. Explain your answer by means of relevant diagrams and equations.What is difference between a 120V/240V step-up and 240/120 V step-down single phase transformers? Both transformers are rated 5 kVA and operated at 60 Hz. Explain your answer by means of relevant diagrams and equations.What is difference between a 120V/240V step-up and 240/120 V step-down single...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage side: ?? = 57.6??, ?? = 16.34??, ??? = 2.784? and ??? = 3.5?. If a load of ????? = 16∠30°? connected to the low-voltage side: a) Find the voltage regulation? b) Draw the phasor diagram? c) Find the efficiency of the transformer? d) Repeat part a and b at ????? = 16∠ − 30°??
A plug-in transformer supplies 9.00 V to a video game system. How many turns are in its secondary coil if its input voltage is 120 V and the primary coil has 381 turns?
(A) A plug-in transformer supplies 9.00 V to a video game system. How many turns are in its secondary coil if its input voltage is 120 V and the primary coil has 381 turns? What is its input current when its output is 1.33 A? (B)What is the characteristic time constant of a 24.2 mH inductor that has a resistance of 4.08 Ω? If it is connected to a 12.0 V battery, what is the current after 12.5 ms? (C)Two...
Let V be the set of all ordered pairs of real numbers. Consider the following addition...
Let V be the set of all ordered pairs of real numbers. Consider the following addition and scalar multiplication operations V. Let u = (u1, u2) and v = (v1, v2). Show that V is not a vector space. • u ⊕ v = (u1 + v1 + 1, u2 + v2 + 1 ) • ku = (ku1 + k − 1, ku2 + k − 1) 1)Show that the zero vector is 0 = (−1, −1). 2)Find the...
A star-connected induction motor has the following rated parameters: Voltage UN = 400 V, current IN...
A star-connected induction motor has the following rated parameters: Voltage UN = 400 V, current IN = 8 A, frequency fN = 50 Hz, speed nN = 1480 rpm, power factor cos ijN = 0.8, efficiency ȘN = 0.9, magnetizing inductance Lm = 280 mH, stator leakage inductance LVı = 9 mH and rotor leakage inductance LUı = 14 mH. For the rated operating point of the motor, calculate the per-unit values for electric active power Pel, mechanical power Pmech,...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following parameter values in Ω/phase referred to the stator: R1 = 0.3 Ω. R2' = 0.15 Ω X1 = 0.5 Ω. X2'= 0.21 Ω Xm = 13.25 Ω The total rotational losses are 450 W. The core loss is lumped in with the rotational losses. For a slip of 0.02, and based on approximate equivalent circuit, determine: (i) The rotor speed. (ii) The stator current....
A 440-V, 3-φ 50-Hz, 4 poles, 37.3 kW, Y-connected induction motor has the following parameters: R1=...
A 440-V, 3-φ 50-Hz, 4 poles, 37.3 kW, Y-connected induction motor has the following parameters: R1= 0.1 Ω, X1 = 0.4 Ω , R2′ = 0.15 Ω , X2′ = 0.44 Ω Motor has stator core loss of 1250 W and rotational loss of 1000 W. It draws a no-load line current of 20 A at a p.f. of 0.09 (lag). When motor operates at a slip of 3%, calculate a. input line current and p.f. [57.4@29°A, 0.875 lag] b....
A three-phase, 11.2-kW, 1750-rpm, 460-V, 60-Hz, four-pole, Y-connected induction motor has the following parameters: Rs =...
A three-phase, 11.2-kW, 1750-rpm, 460-V, 60-Hz, four-pole, Y-connected induction motor has the following parameters: Rs = 0.53 Ω, R’r = 0.38 Ω, Xs = 1.23 Ω, X’r = 1.45 Ω, and Xm = 25.2 Ω. The motor is controlled by varying both the voltage and frequency. The volts/hertz ratio, which corresponds to the rated voltage and rated frequency, is maintained constant. a) Calculate the maximum torque, Tm and the corresponding speed, ꞷm for 60 Hz and 30 Hz. b) Repeat...