In: Electrical Engineering
The 500 KVA, 69kV/11kV, 60 Hz transformer has total resistance Rp of 100 Ω and total leakage reactance of Xp of 600 Ω. Calculate
The per unit impedance of the transformer in percent (just magnitude)
The voltage regulation of the transformer when it delivers 200 KVA with a lagging power
factor of 90% while the secondary voltage is fixed at 11 kV.
The actual primary voltage V1.
The actual line current I1.
Given KVA = 500 KVA
Primary Voltage = V1 = 69 KV
Secondary Voltage = V2 = 11 KV
Rp = 100 Ohms
Xp = 600 Ohms
Impedance Zp = √ Rp2 +Xp2 = √ 1002 +6002 = 608.3 Ohms
Primary Current = KVA/kV1 = 500/69 = 7.24 Amperes
Base Impedance = Zb = Primary Voltage / Primary Current = 69000 / 7.24 = 9530 Ohms
Per Unit Impedance = Zpu = Zb/Zp = 608.3/9530 = 0.064 pu
Transformation Ratio = K = V2/V1 = 11000/69000 = 0.159
Now,
Given load = 200 KVA
Secondary Current = I2 = 200/V2 = 200/11 = 18.18 Ampers
Primary current = I1 = I2*K = 18.18*0.159 = 2.89 Amperes
Power factor = Cos(x) =0.9
Sin(x) = √ 1-sin(x)2 = √ 1-0.92 = 0.435
Primary Voltage = 69000 Volts
Actual Primary Voltage = V = V1 + (I1*Rp*cos(x) ) + (I1*Xp*sin(x) )
V= 69000 + (2.89*100*09) + (2.89*600*0.435)
V = 70014.4 Volts
Voltage regulation = V-V1 / V1 = (70014.4-69000) / 69000 = 0.0147
Percentage voltage regulation = Voltage Regulation*100 = 0.014 *100 = 1.47 percent.
Actual primary line Current = 2.89 Amperes
Actual Primary voltage = 70014.4 Volts