Question

In: Electrical Engineering

The 500 KVA, 69kV/11kV, 60 Hz transformer has total resistance Rp of 100 Ω and total...

The 500 KVA, 69kV/11kV, 60 Hz transformer has total resistance Rp of 100 Ω and total leakage reactance of Xp of 600 Ω. Calculate

  1. The per unit impedance of the transformer in percent (just magnitude)

  2. The voltage regulation of the transformer when it delivers 200 KVA with a lagging power

    factor of 90% while the secondary voltage is fixed at 11 kV.

  3. The actual primary voltage V1.

  4. The actual line current I1.

Solutions

Expert Solution

Given KVA = 500 KVA

Primary Voltage = V1 = 69 KV

Secondary Voltage = V2 = 11 KV

Rp = 100 Ohms

Xp = 600 Ohms

Impedance Zp = Rp2 +Xp2 = 1002 +6002 = 608.3 Ohms

Primary Current = KVA/kV1 = 500/69 = 7.24 Amperes

Base Impedance = Zb = Primary Voltage / Primary Current = 69000 / 7.24 = 9530 Ohms

Per Unit Impedance = Zpu = Zb/Zp = 608.3/9530 = 0.064 pu

Transformation Ratio = K = V2/V1 = 11000/69000 = 0.159

Now,

Given load = 200 KVA

Secondary Current = I2 = 200/V2 = 200/11 = 18.18 Ampers

Primary current = I1 = I2*K = 18.18*0.159 = 2.89 Amperes

Power factor = Cos(x) =0.9

Sin(x) = 1-sin(x)2 = 1-0.92 = 0.435

Primary Voltage = 69000 Volts

Actual Primary Voltage = V = V1 + (I1*Rp*cos(x) ) + (I1*Xp*sin(x) )

V= 69000 + (2.89*100*09) + (2.89*600*0.435)

V = 70014.4 Volts

Voltage regulation = V-V1 / V1 = (70014.4-69000) / 69000 = 0.0147

Percentage voltage regulation = Voltage Regulation*100 = 0.014 *100 = 1.47 percent.

Actual primary line Current = 2.89 Amperes

Actual Primary voltage = 70014.4 Volts


Related Solutions

A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of...
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of 0.56 , 33 and 5.57 respectively. For 10 degree increments of power-factor angle, tabulate and plot percent regulation, and efficiency. Power factor for operation between 0.5 lagging and 0.5 leading.
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows: RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ. The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit. Problem...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100...
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100 kVA with Zeq = 0.5 + j0.8 Ohm. If an autotransformer is built from this conventional transformer to supply a load at 2640V with supply voltage 2400V. Draw the autotransformer and calculate Zeq, the voltage, current and apparent power rating of the auto transformer. Also calculate the apparent power rating advantage of autotransformer over conventional transformer.
345 kV, 50 Hz, 3-phase transmission line is 100 km long. The resistance is 0.048 Ω/km...
345 kV, 50 Hz, 3-phase transmission line is 100 km long. The resistance is 0.048 Ω/km and the inductance is 1,24 mH/km. The shunt capacitance is 0.0174 μF/km. The receiving end load is 216 MW with 0.8 power factor lagging at 325 kV. (a) Compute ABCD parameters using π equivalent circuit (b) Sending end voltage VS, (c) Sending end current IS, (d) Efficiency
Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with...
Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with a 50-Hz, 50-kVA, star-star transformer bank of vector group Yy0. Both have a bank ratio of 2000/200-V. The equivalent impedances referred to the respective secondaries are ZΔ = 0.1106/60.2° Ω and ZY = 0.0369/60.2° Ω. (a) Assuming the load switch to be open, draw the connection diagram   (3.0 marks). (b) Determine the magnitude of the current circulating in each transformer secondary   (15.0 marks). (c)...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is adjustable from no load to 120 percent rated KVA. The percent resistance, percent reactance, and percent core loss are m+1.56, m+3.16, and m+0.42 respectively. For 2 KVA increments of load, tabulate and plot the efficiency of the transformer from no load to 120 percent rated load. Use Matlab n=20 m=.2
A current transformer rated 500/5 A, 20 VA, 50 Hz has a turns ratio of 1:99....
A current transformer rated 500/5 A, 20 VA, 50 Hz has a turns ratio of 1:99. Its resistance aand leakage reluctance of the secondary winding are 0.4 Ω and 0.35 Ω respectively. At rated non-inductive burden, the inphase and quadrature components of the exciting mmf are 6 AT and 8 AT respectively. Determine the current and phase angle error.
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT