Question

In: Electrical Engineering

The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...

The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor.

No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W

Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW

Stator resistance between line terminals = 2.34 Ω.

Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage and frequency with a slip of 2.8 percent.

Solutions

Expert Solution


Related Solutions

A 3 phase 460 V, 60 Hz, 4 pole, delta connected induction motor has the following...
A 3 phase 460 V, 60 Hz, 4 pole, delta connected induction motor has the following equivalent circuit parameters. Rs = 0.42 Ω, Rr = 0.23 Ω, Xs = Xr = 0.82 Ω. Xm = 22 Ω. The no load loss = 60 W and may be assumed constant. The rotor speed is 1750 rpm. Use the approximate equivalent circuit ( i.e. the Xm branch is at the very left of the circuit) determine the following a. the synchronous speed...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following parameter values in Ω/phase referred to the stator: R1 = 0.3 Ω. R2' = 0.15 Ω X1 = 0.5 Ω. X2'= 0.21 Ω Xm = 13.25 Ω The total rotational losses are 450 W. The core loss is lumped in with the rotational losses. For a slip of 0.02, and based on approximate equivalent circuit, determine: (i) The rotor speed. (ii) The stator current....
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
Problem 5: The following data refers to a 10-pole, 200 V, 50 Hz, 3 phase induction...
Problem 5: The following data refers to a 10-pole, 200 V, 50 Hz, 3 phase induction motor? R1 = 3.5 ohm, X1 = 11 ohm, R`2 = 13.2 ohm. When the motor is tested on no-load, its observed that it takes 7.6 A (line current) and the total core loss is 620 W. B y using an approximate equivalent circuit at 8% slip, Calculate; The rotor current The supply current and power factor Mechanical power developed. Gross load torque Determine...
A 400V, 2 pole, 50 Hz, three-phase induction motor is drawing 60 A at 0.85 PF...
A 400V, 2 pole, 50 Hz, three-phase induction motor is drawing 60 A at 0.85 PF lagging. The stator copper losses are 2 kW, the stator core losses are 1.8 kW and rotor copper losses are 700 W. The friction and windage losses are 600 W, the stray loss 100 W, and rotor core loss 100 W. Find the following quantities: a. The air gap power. b. The developed mechanical power. c. The output power. d. The efficiency of the...
A   three-phase,   460-V,   60-Hz,   six-pole   Y-connected   induction   motor   has   Rs = 0.32 Ω, R′ r =...
A   three-phase,   460-V,   60-Hz,   six-pole   Y-connected   induction   motor   has   Rs = 0.32 Ω, R′ r = 0.18 Ω, Xs = 1.04 Ω, X′ r = 1.6 Ω,   and   Xm = 18.8 Ω.   The   no-load   loss,   Pno load,   is   negligible.   The   load   torque,   which   is   proportional   to   speed   squared,   is   180 N#m   at   1180   rpm.   If   the   motor   speed   is   850   rpm,   determine   (a)   the   load   torque   demand   TL; (b)   the   rotor   current   I′ r; (c)   the   stator   supply   voltage   Va;...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A 400 V,50 Hz, six-pole three-phase induction motor drives a constant load of 140 N.m. The...
A 400 V,50 Hz, six-pole three-phase induction motor drives a constant load of 140 N.m. The motor has the following parameters ?1=0.294 Ω ?1=1.39 ?? ??=41 ?? ?2′=0.156 Ω ?2′=0.74 ?? 1) Starting. Calculate the following: i) Motor starting current. ii) Motor starting torque. 2) Maximum operating point. Calculate the following: i) Slip at which maximum torque is developed. ii) Maximum torque developed. 3) Steady-state operation. Calculate the following: i) Motor slip. ii) Motor speed. iii) Motor current. iv) Motor...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The following results were obtained from open circuit (no-load) and short circuit tests.             Open Circuit (no-load) Test Applied Stator Voltage VLine (V) Stator Line Current ILine (A) Total Input Power Pin (W) 240 9.6 536 220 7.2 420 200 5.4 352 180 4.3 304 160 3.5 276 140 3.0 248 120 2.5 224             Short Circuit (locked rotor) Test Applied Stator Voltage VLine (V) Stator Line...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...