Question

In: Electrical Engineering

QUIESTION 1 A three-phase synchronous generator is connected to an infinite bus. The infinite bus voltage...

QUIESTION 1
A three-phase synchronous generator is connected to an infinite bus. The infinite bus voltage and the generated voltage are o 1.0 pu ∠0 and o 1.0pu ∠42.84 , respectively. The synchronous reactance is 0.85 pu and resistances are neglected. a) Compute power angle (δ), armature current (Is), power factor (pf), real power (P), and reactive power (Q). Draw the phasor diagram. b) If the prime mover torque is kept constant at a value corresponding to P=0.8 pu, compute the required value of the generated voltage (E2) for the unity power factor condition (and constant power, P=0.8 pu). What is the new value of power angle (δ2)? Solution: δ= 42.84o , Is = 0.86pu ∠21.44o , pf=0.93, P=0.8 ph, Q= -0.314pu, δ2 = 34.2o , E2= 1.21pu

QUESTION 2
Two “three-phase Y-connected synchronous generators” have per phase generated voltages of o 1 E = 120 V∠10 and o 2 E = 120 V∠20 under no load, and resistance of X j5 Ω / phase 1 = and X j8 Ω / phase 2 = . They are connected in parallel to a load impedance of XL = 4 + j3 Ω / phase . Compute: a) Per phase terminal voltage Vt (both magnitude and phase angle). b) Armature currents for each generator ( a1 a2 I and I ). c) Power supplied by each generator (P1 and P2 ). d) The total output power (Pout ). Solution: Vt= 82 V ∠-5.94o , Ia1 = 9.36 A ∠-51.17o , Ia2 = 7.31 A ∠-32.06o , P1 = 1621 W, P2 = 1614.5 W, Pout = 3236 W.

Solutions

Expert Solution


Related Solutions

A 1000MVA, 20kV, 60 Hz three phase generator is connected to an infinite bus through a...
A 1000MVA, 20kV, 60 Hz three phase generator is connected to an infinite bus through a 1000MVA, 20kV? / 345kVY transformer to a 345kV circuit breaker and a 345kV transmission line. The generator reactances are X``d=0.17, X`d=0.30, and Xd=1.5 per unit on a 1000MVA, 20kV base. Generator time constants are T``d=0.05 seconds, T`d=1.0 seconds, and TA=0.10 seconds. The transformer series reactance is 0.10 per unit on the transformer ratings as a base. Neglect transformer losses, excitation current, and transformer time...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
A 50 Hz synchronous generator is supplying 60% of its maximum power to an infinite bus...
A 50 Hz synchronous generator is supplying 60% of its maximum power to an infinite bus through a reactive network. Due to a certain fault, the reactance of the network between the generator internal voltage and the infinite bus is increased four times. After the fault is cleared, 80% of maximum power can be transferred Sketch the mechanical power vs. power angle curves, in the same figure, under the different operation conditions, and annotate all the key points on the...
Consider the classical power system where one generator is connected to the infinite bus through two...
Consider the classical power system where one generator is connected to the infinite bus through two transmission lines. We want to study the transient stability for a fault on one of the two lines. The generator parameters are as follows: Pm = 1, H = 4, KD = 5, x'd = 0.25, E' =1.4. The transmission line where the fault occurs has a line reactance of 0.6 pu. The other transmission line that remains in service has a line reactance...
A synchronous generator has parameters as shown in table below. 1. Voltage Rating 30 kV, 3-phase...
A synchronous generator has parameters as shown in table below. 1. Voltage Rating 30 kV, 3-phase 5. Frequency 50 Hz 2. Power Rating 50 MVA 6. Rotor Round 3. Synchronous Reactance, XS 7 Ω /phase 7. Connection STAR 4. Armature resistance, Ra 1.5 Ω /phase 8. Excitation Type Permanent Magnet An inductive load of 30MW at 0.8 power factor at rated terminal voltage is connected to the synchronous generator to an infinite bus. Determine the excitation voltage per phase and...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following: a.The speed of rotation of the generator at full load. b.The voltage regulation of the generator. c.The developed torque on the shaft of the generator....
Given a balanced three-phase delta-connected generator with positive sequence and voltage Vbc=350∠−90∘Vbc=350∠−90∘ Vrms. The generator feeds...
Given a balanced three-phase delta-connected generator with positive sequence and voltage Vbc=350∠−90∘Vbc=350∠−90∘ Vrms. The generator feeds a balanced three-phase delta-connected load having an impedance of 43.5+j27 Ω/phase. The impedance of the line connecting the generator to the load is 1.5+j1 Ω/phase.  i) Calculate the total real power consumed by the load. [5] ii) Calculate the percentage of the total available real power lost in the lines.[3]   
Present the single-phase equivalent circuit of a synchronous generator.
Present the single-phase equivalent circuit of a synchronous generator.
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a Y-connected load. The transmission line has an impedance of (0.02+j0.4) Ω/phase, and the load has an impedance of (4+j3) Ω per phase. Determine the;(a)line current (IL) at the load [2Marks] (b)line and phase voltage of the load[2 Marks](c)active power, reactive and apparent power [2 Marks](d) power factor and specify whether it is lagging or leading. [4 Marks]
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT