The equivalent synchronous impedance of a 25kVA,
400V
three-phase Y-connected synchronous generator is 0.05 + j1.6
ohm.
When the rated voltage was output under no load, the rated current
flowed by connecting the load.
Part a)
If the load power factor is 0.8, 1.0 lagging, and 0.8
lagging,
calculate the pull-up voltage, load angle, and voltage fluctuation
rate for each.
Ignore the magnetic saturation.
Part b)
If the power factor is 0.8, 1.0 lagging and 0.8 leading,
when the rated...