Question

In: Electrical Engineering

A 50 Hz synchronous generator is supplying 60% of its maximum power to an infinite bus...

A 50 Hz synchronous generator is supplying 60% of its maximum power to an infinite bus through a reactive network. Due to a certain fault, the reactance of the network between the generator internal voltage and the infinite bus is increased four times. After the fault is cleared, 80% of maximum power can be transferred
Sketch the mechanical power vs. power angle curves, in the same figure, under the different operation conditions, and annotate all the key points on the curves
Calculate the power angle before which the fault shouldbe cleared to avoid the generator instability

A 50 Hz synchronous generator is supplying 60% of its maximum power to an infinite bus through a reactive network. Due to a certain fault, the reactance of the network between the generator internal voltage and the infinite bus is increased four times. After the fault is cleared, 80% of maximum power can be transferred
Sketch the mechanical power vs. power angle curves, in the same figure, under the different operation conditions, and annotate all the key points on the curves
Calculate the power angle before which the fault shouldbe cleared to avoid the generator instability

Solutions

Expert Solution

Please Kindly follow the attachments................


Related Solutions

A 1000MVA, 20kV, 60 Hz three phase generator is connected to an infinite bus through a...
A 1000MVA, 20kV, 60 Hz three phase generator is connected to an infinite bus through a 1000MVA, 20kV? / 345kVY transformer to a 345kV circuit breaker and a 345kV transmission line. The generator reactances are X``d=0.17, X`d=0.30, and Xd=1.5 per unit on a 1000MVA, 20kV base. Generator time constants are T``d=0.05 seconds, T`d=1.0 seconds, and TA=0.10 seconds. The transformer series reactance is 0.10 per unit on the transformer ratings as a base. Neglect transformer losses, excitation current, and transformer time...
QUIESTION 1 A three-phase synchronous generator is connected to an infinite bus. The infinite bus voltage...
QUIESTION 1 A three-phase synchronous generator is connected to an infinite bus. The infinite bus voltage and the generated voltage are o 1.0 pu ∠0 and o 1.0pu ∠42.84 , respectively. The synchronous reactance is 0.85 pu and resistances are neglected. a) Compute power angle (δ), armature current (Is), power factor (pf), real power (P), and reactive power (Q). Draw the phasor diagram. b) If the prime mover torque is kept constant at a value corresponding to P=0.8 pu, compute...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and Its rated Line current is 100 A. if the generator is connected to a 480V grid Draw the phasor diagram and find EA, delta angle and output power under the following conditions a- The generator supply the rated current at 0.8 PF lagging. b-The generator supply the rated current at 1.0 PF. c- The generator supply the rated current at 0.8 PF leading.
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
Consider the classical power system where one generator is connected to the infinite bus through two...
Consider the classical power system where one generator is connected to the infinite bus through two transmission lines. We want to study the transient stability for a fault on one of the two lines. The generator parameters are as follows: Pm = 1, H = 4, KD = 5, x'd = 0.25, E' =1.4. The transmission line where the fault occurs has a line reactance of 0.6 pu. The other transmission line that remains in service has a line reactance...
How is the active power regulated in a synchronous generator?
How is the active power regulated in a synchronous generator?
A synchronous generator is delivering 35% of the power that is capable of delivering to an...
A synchronous generator is delivering 35% of the power that is capable of delivering to an infinite bus. If the electrical power of the generator is doubled, determine the maximum value of rotor angle during the swinging of the generator around its new equilibrium position. Draw the corresponding power angle curve.
Consider a salient-role generator delivering power through a short transmission line to an infinite bus V∞=1∠0°,...
Consider a salient-role generator delivering power through a short transmission line to an infinite bus V∞=1∠0°, |Ea|=1.5. The active power delivered to the infinite bus is 0.7. We are given the generator reactances Xd=1.6 and Xq=1.0 and the line reactance XL=0.3. Neglect resistances, draw the phasor diagram and find Ea and Ia.
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....