Question

In: Electrical Engineering

Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...

Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following:
a.The speed of rotation of the generator at full load.
b.The voltage regulation of the generator.
c.The developed torque on the shaft of the generator.
d.The efficiency of the generator at full load.

Solutions

Expert Solution


Related Solutions

A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance...
A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance of 0.6 and negligible armature resistance. Its friction, windage and core losses are 1.2KW, 0.5KW and 1KW respectively . What is the speed of this motor? If this motor is initially supplying rated hp at 0.82 PF lagging . What are the magnitudes and angles of ? What is the power factor of the motor? How much induced torque and load torque is produced...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24 ohms per phase. The armature resistance may be ignored. This motor is energized from 3.3-kV infinite bus bars. The field excitation is adjusted until unity power factor at rated load is achieved. Compute the maximum power and torque that the motor can deliver with the excitation remaining unchanged
Consider two equal non sallent pole three phase 60 cycle Y connected 6600 volt 10000-kva synchronous...
Consider two equal non sallent pole three phase 60 cycle Y connected 6600 volt 10000-kva synchronous generators, each wuth an effective resistance of 0.063 ohm per phase and a synchronous reactance of 1.52 ohm per phase. Assume that the resistances and reactances of the generators are constant. These generators in parallel carry an inductive load of 18000 kva at 0.9 power factor. (a) find the excitation voltages of the generators and their power angles when they share the kw load...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3...
Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 420+300i Ω/ϕ ; load 2 is Δ-connected with an impedance of 2400-1780i Ω/ϕ ; and load 3 is 170.1+2201i kVA . The loads are fed from a distribution line with an impedance of 2+17i Ω/ϕ . The magnitude of the line-to-neutral voltage at the load end of the line is 23√3 kV. Part A: Calculate the total complex power at the sending end of...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT