Question

In: Electrical Engineering

A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...

A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0
Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and
core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R
losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V.
a. What is the speed of rotation of this generator?
b. What is the terminal voltage of the generator if :

i.
ii.
iii.
it is loaded with the rated current at 0.8 PF lagging;
it is loaded with the rated current at 1.0 PF;
it is loaded with the rated current at 0.8 PF leading.

c. What is the efficiency of this generator (ignoring the unknown electrical losses) when it is operating
at the rated current and 0.8 PF lagging?
d. How much shaft torque must be applied by the prime mover at the full load? how large is the induced
counter-torque?
e. What is the voltage regulation of this generator at
i. 0.8 PF lagging ii. at Unity PF iii. at 0.8 PF leading?
a. The figure below is a set of Synchronous Generator and Synchronous Motor. The ratings of the
machines are as follows:
Synchronous Generator: . 3ph, 1.0 MVA, 2.3kV, 50Hz, 0.85 lagging power factor, Xs =0.9 pu
Synchronous Motor: 3ph, 0.5 MVA, 2.3kV, 50Hz, 0.85 leading power factor, Xs =0.8 pu
The generator is equipped with a voltage regulator which maintains the terminal voltage at the rated value.
The motor delivers 500 hp and it field current is adjusted to make it operate at unity power factor.

i.
ii.
iii.
Determine the synchronous reactance in ohms.
Determine the excitation voltage of each machine.
Draw the phasor diagrams

a. The figure below is a set of Synchronous Generator and Synchronous Motor. The ratings of the
machines are as follows:
Synchronous Generator: . 3ph, 1.0 MVA, 2.3kV, 50Hz, 0.85 lagging power factor, Xs =0.9 pu
Synchronous Motor: 3ph, 0.5 MVA, 2.3kV, 50Hz, 0.85 leading power factor, Xs =0.8 pu
The generator is equipped with a voltage regulator which maintains the terminal voltage at the rated value.
The motor delivers 500 hp and it field current is adjusted to make it operate at unity power factor.

The following test results are obtained for a 3ph, 25 kV, 750 MVA, 50 Hz, 3600rpm, star-connected
synchronous machines at rated speed.

i. Determine the unsaturated and saturated values of the synchronous reactance in ohms and pu.
If a short-circuit test is performed at constant field current 1500 A but at different speeds; 1000, 2000, 3000
and 3600 rpm.
Determine the short-circuit current at these speeds above.
Determine the field current if the synchronous machine delivers rated MVA to an infinite bus at 0.9 lagging
power factor
ii.
iii.

If=1500A VLL(Open circuit)=25KV, IA(open circuit test)=10000A,VLL(air gap line)=30KV


g. Calculate the capacitance of a square parallel plate capacitor having two
dielectrics εr1=2.5 and εr2=3.5 each comprising one half of the area between
the plates. The area of a plate is 4.0 x 104 cm2 and the two plates separated by
a distance of 20mm.
h. If a 24V volts electric potential is applied across the terminals of this
capacitor described above, find the electric potential energy stored in the
capacitor.

please answer these for me

Solutions

Expert Solution


Related Solutions

A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and Its rated Line current is 100 A. if the generator is connected to a 480V grid Draw the phasor diagram and find EA, delta angle and output power under the following conditions a- The generator supply the rated current at 0.8 PF lagging. b-The generator supply the rated current at 1.0 PF. c- The generator supply the rated current at 0.8 PF leading.
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24 ohms per phase. The armature resistance may be ignored. This motor is energized from 3.3-kV infinite bus bars. The field excitation is adjusted until unity power factor at rated load is achieved. Compute the maximum power and torque that the motor can deliver with the excitation remaining unchanged
A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance...
A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance of 0.6 and negligible armature resistance. Its friction, windage and core losses are 1.2KW, 0.5KW and 1KW respectively . What is the speed of this motor? If this motor is initially supplying rated hp at 0.82 PF lagging . What are the magnitudes and angles of ? What is the power factor of the motor? How much induced torque and load torque is produced...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following: a.The speed of rotation of the generator at full load. b.The voltage regulation of the generator. c.The developed torque on the shaft of the generator....
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A 3-phase, 380 V, 50 Hz , 6 pole, Y-connected induction motor has R1 = 0.1...
A 3-phase, 380 V, 50 Hz , 6 pole, Y-connected induction motor has R1 = 0.1 W , X1 = 0.4 W, R2’ = 0.12 W , X2’ = 0.4 W, Xm = 20 W , Pr = 1 kW. The motor is operated at 970 rpm what is the efficiency?
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following parameter values in Ω/phase referred to the stator: R1 = 0.3 Ω. R2' = 0.15 Ω X1 = 0.5 Ω. X2'= 0.21 Ω Xm = 13.25 Ω The total rotational losses are 450 W. The core loss is lumped in with the rotational losses. For a slip of 0.02, and based on approximate equivalent circuit, determine: (i) The rotor speed. (ii) The stator current....