The equivalent synchronous impedance of a 25kVA, 400V three-phase Y-connected synchronous generator is 0.05 + j1.6...

The equivalent synchronous impedance of a 25kVA, 400V
three-phase Y-connected synchronous generator is 0.05 + j1.6 ohm.
When the rated voltage was output under no load, the rated current flowed by connecting the load.
Part a)
If the load power factor is 0.8, 1.0 lagging, and 0.8 lagging,
calculate the pull-up voltage, load angle, and voltage fluctuation rate for each.
Ignore the magnetic saturation.

Part b)
If the power factor is 0.8, 1.0 lagging and 0.8 leading,
when the rated current flows through the generator at the rated output voltage,
calculate the internal induced power, load angle, and voltage dynamic for each.

Answer
Part a)
190.4V, 11.26 deg, 21.3%
221.8V, 14.47 deg, 4.1%
259.2V, 11.82 deg, -11.3%

Part b)
270.8V, 9.59 deg, 17.5%
239.8V, 13.93 deg, 3.8%
203.3V, 13.45 deg -12.0%

Solutions

Expert Solution


Related Solutions

Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following: a.The speed of rotation of the generator at full load. b.The voltage regulation of the generator. c.The developed torque on the shaft of the generator....
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
Present the single-phase equivalent circuit of a synchronous generator.
Present the single-phase equivalent circuit of a synchronous generator.
Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced three-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 420+300i Ω/ϕ ; load 2 is Δ-connected with an impedance of 2400-1780i Ω/ϕ ; and load 3 is 170.1+2201i kVA . The loads are fed from a distribution line with an impedance of 2+17i Ω/ϕ . The magnitude of the line-to-neutral voltage at the load end of the line is 23√3 kV. Part A: Calculate the total complex power at the sending end of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
QUIESTION 1 A three-phase synchronous generator is connected to an infinite bus. The infinite bus voltage...
QUIESTION 1 A three-phase synchronous generator is connected to an infinite bus. The infinite bus voltage and the generated voltage are o 1.0 pu ∠0 and o 1.0pu ∠42.84 , respectively. The synchronous reactance is 0.85 pu and resistances are neglected. a) Compute power angle (δ), armature current (Is), power factor (pf), real power (P), and reactive power (Q). Draw the phasor diagram. b) If the prime mover torque is kept constant at a value corresponding to P=0.8 pu, compute...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4 Ω per phase. The magnitude of the line current ILis:
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a Y-connected load. The transmission line has an impedance of (0.02+j0.4) Ω/phase, and the load has an impedance of (4+j3) Ω per phase. Determine the;(a)line current (IL) at the load [2Marks] (b)line and phase voltage of the load[2 Marks](c)active power, reactive and apparent power [2 Marks](d) power factor and specify whether it is lagging or leading. [4 Marks]
A three phase synchronous motor is Y-connected with the following values: 2.3 kV, 400 hp, 60...
A three phase synchronous motor is Y-connected with the following values: 2.3 kV, 400 hp, 60 Hz, 8 poles with a rated pf of 0.85 leading. It is 90% efficient at full load with an armature resistance of 0.80 Ohms and synchronous reactance of 11 Ohms. At full load calculate the output torque, and internal generated voltage (EA)
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT