Question

In: Electrical Engineering

A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...

A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following:

a) Its terminal voltage when it is loaded with the rated current at a power factor of 0.9 lagging

b) Its terminal voltage when it is loaded with the rated current at a power factor of 0.9 leading

Hence,

Answer for a (0.9 lagging) should equal VT= 433.59 V

Answer for b (0.9 leading) should equal VT= 512.486 V

Solutions

Expert Solution

Hence I calculated both 0.9 leading and lagging pf terminal voltages


Related Solutions

A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and Its rated Line current is 100 A. if the generator is connected to a 480V grid Draw the phasor diagram and find EA, delta angle and output power under the following conditions a- The generator supply the rated current at 0.8 PF lagging. b-The generator supply the rated current at 1.0 PF. c- The generator supply the rated current at 0.8 PF leading.
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24 ohms per phase. The armature resistance may be ignored. This motor is energized from 3.3-kV infinite bus bars. The field excitation is adjusted until unity power factor at rated load is achieved. Compute the maximum power and torque that the motor can deliver with the excitation remaining unchanged
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following...
Q3) A three-phase, Y-connected, 220 V, 13 kW, 60 Hz, six-pole induction motor has the following parameter values in Ω/phase referred to the stator: R1 = 0.3 Ω. R2' = 0.15 Ω X1 = 0.5 Ω. X2'= 0.21 Ω Xm = 13.25 Ω The total rotational losses are 450 W. The core loss is lumped in with the rotational losses. For a slip of 0.02, and based on approximate equivalent circuit, determine: (i) The rotor speed. (ii) The stator current....
A   three-phase,   460-V,   60-Hz,   six-pole   Y-connected   induction   motor   has   Rs = 0.32 Ω, R′ r =...
A   three-phase,   460-V,   60-Hz,   six-pole   Y-connected   induction   motor   has   Rs = 0.32 Ω, R′ r = 0.18 Ω, Xs = 1.04 Ω, X′ r = 1.6 Ω,   and   Xm = 18.8 Ω.   The   no-load   loss,   Pno load,   is   negligible.   The   load   torque,   which   is   proportional   to   speed   squared,   is   180 N#m   at   1180   rpm.   If   the   motor   speed   is   850   rpm,   determine   (a)   the   load   torque   demand   TL; (b)   the   rotor   current   I′ r; (c)   the   stator   supply   voltage   Va;...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following: a.The speed of rotation of the generator at full load. b.The voltage regulation of the generator. c.The developed torque on the shaft of the generator....
396 v, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous...
396 v, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous reactance. Friction; wind; core losses and armature resistance are neglected. a) If the motor is operating under magnitude of phase current (ia) 216 Ampere and power factor of 0.6 lagging, 1. Find the input power of motor in hp ( 2. Find the generated voltage, EA 3. Find the torque and the maximum inducible torque in current state. b) If EA is increased by...