Consider two equal non sallent pole three phase 60 cycle Y connected 6600 volt 10000-kva synchronous...

Consider two equal non sallent pole three phase 60 cycle
Y connected 6600 volt 10000-kva synchronous generators, each wuth an effective resistance of 0.063 ohm per phase and a synchronous reactance of 1.52 ohm per phase. Assume that the resistances and reactances of the generators are constant. These generators in parallel carry an inductive load of 18000 kva at 0.9 power factor. (a) find the excitation voltages of the generators and their power angles when they share the kw load equally and operate at the same power factor. (b0 assume that the power laod on generator a is increased by adjusting the gpbernors on the prime movers, keeping the frequency the same, until generator a carries two thirds of the load on the system. The excitation of generator a is kept constant, but the excitation of generator B is adjusted to keep the terminal voltage of the system 6000 volts. Under these new conditions find the excitation voltage of generator B and the new power angles.

Solutions

Expert Solution

Answer:-

given that:

Two equal non-salient 3 phase 60HZ, Y-connected

Load:- 18000 KVA at 0.9 PF lagging.

a) when the two generator share's equal load

generator power

Armature Current

  

  

Phasor Armature current

Negative sign due to lagging PF.

a) Excitation Voltage

Phase value

Line value

From the above phasor voltage

Power Angle

Note:- All the value is calculated in this condition are same for both generator A& B.

b) Load on generator A is increase to 2/3 of rated load.

-excitation voltage kept constant.

  -generator B terminal voltage 6600v

Power delivered by generator B during above condition

at same PF that is 0.9 lagging

Armature current of generator(B)

  

Ampere/phase

New excitation voltage ()

New excitation voltage of generator B

Line voltage of generator B

Power angle


Related Solutions

A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has...
480 V, 200 kVA, 08 PF lagging, 60 Hz two pole Y connected synchronous generator has a synchronous reactance of 0.25 Ω and an armature resistance of 0.03 Ω. At 60 Hz, its friction and windage losses are 6 kW, and its core losses are 4 kW. The field circuit has a dc voltage of 200 V, and the maximum IF is 10 A. The resistance of the field circuit is adjustable over the range from 20 to 200 Ω....
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A three phase synchronous motor is Y-connected with the following values: 2.3 kV, 400 hp, 60...
A three phase synchronous motor is Y-connected with the following values: 2.3 kV, 400 hp, 60 Hz, 8 poles with a rated pf of 0.85 leading. It is 90% efficient at full load with an armature resistance of 0.80 Ohms and synchronous reactance of 11 Ohms. At full load calculate the output torque, and internal generated voltage (EA)
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1...
Q4- A 480V, 50Hz, 20KVA Y-connected eight-pole synchronous generator has a per-phase synchronous impedance of 0.15+??1.1 ?. The total mechanical and stray losses are 1.5kW. The core losses are neglected. Assume that the magnetization curve of the generator is linear. If the generator operates at full load at a unity power factor, calculate the following: a.The speed of rotation of the generator at full load. b.The voltage regulation of the generator. c.The developed torque on the shaft of the generator....
1. 414 Volt, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω...
1. 414 Volt, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous reactance. Friction; wind; core losses and armature resistance are neglected. a) If the motor is operating under magnitude of phase current (ia) 234 Ampere and power factor of 0.6 lagging, 1. Find the input power of motor in hp (10p) 2. Find the generated voltage, EA (10p) 3. Find the torque and the maximum inducible torque in current state. (10p) b) If EA...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24 ohms per phase. The armature resistance may be ignored. This motor is energized from 3.3-kV infinite bus bars. The field excitation is adjusted until unity power factor at rated load is achieved. Compute the maximum power and torque that the motor can deliver with the excitation remaining unchanged
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor. No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW Stator resistance between line terminals = 2.34 Ω. Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT