Question

In: Electrical Engineering

A three phase transformer of 400kVA, 10kV/400V, Dy11 is connected to its nominal load with cosφ...

A three phase transformer of 400kVA, 10kV/400V, Dy11 is connected to its nominal load with cosφ = 1.

a) Calculate the nominal primary and secondary line current.
b) Calculate the corresponding currents in the primary and secondary winding.

At an open circuit test, the primary line current is 0,52A with cosφ = 0,05 at nominal line voltage.
The short circuit test (at nominal current) shows 214V primary line voltage and P=1,333kW per phase.

c) Calculate the total iron losses and total copper losses of this transformer.

d) Calculate the efficiency η of this transformer.

Now the transformer will be loaded with 210kW with cosφ = 0,83 (lagging).

e) Give both the iron losses and the copper losses as a percentage of what they are nominally.

Please show process and computations with comments.

Solutions

Expert Solution


Related Solutions

A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission...
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission line. The line-line voltage for the source is 100∟0° V/phase and the impedance of load is (27 + j18) Ω/phase. The transmission line has an impedance of (1 + j4) Ω/line. a) Draw the complete schematic of the power system showing the location of wattmeters. (Two-Wattmeter system is considered for this problem). Phase “a” could be considered as a reference phase. b) What must...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The load impedances are Za = 14+j3 Ω , Zb = 5-j24Ω and Zc =1+j14 Ω  and the phase a line voltage has an effective value of 18 Kv: use line-to-neutral voltage of phase A as a reference. Find the line and neutral current, also find the reactive power delivered to load and power factor.
b) The load connected to a three-phase supply comprises three similar coils connected in star. If...
b) The load connected to a three-phase supply comprises three similar coils connected in star. If the phase currents are 10A and the total active power and power factor absorb by the loads are 3kW and 0.8 lagging, respectively. Find: i. The magnitude of phase and line voltages ii. Total apparent power (1 mark) iii. The impedance of each coil. c) If the coil in Q3(b) are now connected in delta to the same three-phase supply, calculate the magnitude of...
A 3phase,400V sourcesupplies a delta connected load having phase impedances Zab=25? 0º ohms, Zbc=25?30º ohms, and...
A 3phase,400V sourcesupplies a delta connected load having phase impedances Zab=25? 0º ohms, Zbc=25?30º ohms, and Zca=25?-30º ohms. The magnitude of all the phase currents is ____ A.
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3...
A three phase transformer of 200MVA, 33kV/380kV, Yd11 is delivering nominal power at cosφ = 1....
A three phase transformer of 200MVA, 33kV/380kV, Yd11 is delivering nominal power at cosφ = 1. Calculate the nominal primary and secondary line current. Calculate the winding ratio n of this transformer. The primary line current is 15,9A during an open circuit test. The measured power per phase is then 53kW. During a short circuit test (at nominal current), 271V primary line voltage is measured at cosφ = 0,225. Calculate the total iron losses and total copper losses of this...
An unbalanced wye connected wye connected load of three phase resistances with Ra=60 ohms, Rb=40 ohms...
An unbalanced wye connected wye connected load of three phase resistances with Ra=60 ohms, Rb=40 ohms and Rc=80 ohms is connected to a 440V, negative sequence, balanced 3 phase, 3 wire supply. Calculate the complex power using the method of symmetrical components. Please show all steps and clearly show all answers.
Question 5 a) Draw the circuit of a Three-phase bridge inverter using a Y-connected load and...
Question 5 a) Draw the circuit of a Three-phase bridge inverter using a Y-connected load and explain its operation using 180 degree conduction clearly showing the gating sequence and the corresponding output line voltages for each phase. (10) b) For the Y-connected load determine the line to neutral voltages for the three modes of operations. Draw the equivalent circuits for each mode and then draw the phase voltage waveforms for the 180-degree conduction. (7)
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4 Ω per phase. The magnitude of the line current ILis:
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed of 1750rpm. The rotational mechanical losses are constant and equal to 500W. The core losses are constant and equal to 300W. The copper losses in the stator equal to the copper losses in the rotor at full load. If the rotor resistance per phase is 0.25?, calculate the following: a.The frequency of the induced current in the rotor circuit at full load. b.The percentage...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT