An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The...

An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The load impedances are Za = 14+j3 Ω , Zb = 5-j24Ω and Zc =1+j14 Ω  and the phase a line voltage has an effective value of 18 Kv: use line-to-neutral voltage of phase A as a reference.

Find the line and neutral current, also find the reactive power delivered to load and power factor.

Solutions

Expert Solution

THANK YOU


Related Solutions

An unbalanced wye connected wye connected load of three phase resistances with Ra=60 ohms, Rb=40 ohms...
An unbalanced wye connected wye connected load of three phase resistances with Ra=60 ohms, Rb=40 ohms and Rc=80 ohms is connected to a 440V, negative sequence, balanced 3 phase, 3 wire supply. Calculate the complex power using the method of symmetrical components. Please show all steps and clearly show all answers.
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission...
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission line. The line-line voltage for the source is 100∟0° V/phase and the impedance of load is (27 + j18) Ω/phase. The transmission line has an impedance of (1 + j4) Ω/line. a) Draw the complete schematic of the power system showing the location of wattmeters. (Two-Wattmeter system is considered for this problem). Phase “a” could be considered as a reference phase. b) What must...
Three equal impedances, (8+j6) ohms are connected in wye across a three-phase, three-wire supply. The symmetrical...
Three equal impedances, (8+j6) ohms are connected in wye across a three-phase, three-wire supply. The symmetrical components of the phase A line voltages are: Va0 = 0 Va1 = 220 + j 28.9 V Va2 = -40 - j 28.9 If there is no connection between the load neutral and the supply neutral, Calculate the symmetrical currents of line a,b, and c.
A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms....
A balanced positive-sequence wye-connected 60-Hz three-phase source has line-to-line voltages of VL = 440 V rms. This source is connected to a balanced wye-connected load. Each phase of the load consists of a 0.5-H inductance in series with a 50-? resistance. Assume that the phase of Van is zero. A) Find the line-to-neutral voltage phasor Van. Enter your answer using polar notation. Express argument in degrees. B) Find the line-to-neutral voltage phasor Vbn. Enter your answer using polar notation. Express...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3...
A balanced three-phase delta-connected source has a line veltage of 120 V. It is connected to...
A balanced three-phase delta-connected source has a line veltage of 120 V. It is connected to a load via a three-wire transmission line. The per-phase impedance of the delta-connected load is 30 + 120j (2. The impedance of each wire of the transmission line is 2 + 4j 2. How much power is dissipated by the load? By the transmission line? What is the power factor of the load? What is the overall power factor?
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4 Ω per phase. The magnitude of the line current ILis:
b) The load connected to a three-phase supply comprises three similar coils connected in star. If...
b) The load connected to a three-phase supply comprises three similar coils connected in star. If the phase currents are 10A and the total active power and power factor absorb by the loads are 3kW and 0.8 lagging, respectively. Find: i. The magnitude of phase and line voltages ii. Total apparent power (1 mark) iii. The impedance of each coil. c) If the coil in Q3(b) are now connected in delta to the same three-phase supply, calculate the magnitude of...
A three-phase balanced star load No. 1 of (120 +j90) ohms in parallel with another three-phase...
A three-phase balanced star load No. 1 of (120 +j90) ohms in parallel with another three-phase balanced star load No. 2 of (90 +j120) ohms, both are fed by three-phase balanced conductors of 3 ohms resistance and 4 ohms reactance. If the generator is 240 volts, with angle of -150° on phase c and reactance of 1 ohms, determine: a) the current on load N°1 on phase C, b) the terminal voltage of the generator on phase B, c) the...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed of 1750rpm. The rotational mechanical losses are constant and equal to 500W. The core losses are constant and equal to 300W. The copper losses in the stator equal to the copper losses in the rotor at full load. If the rotor resistance per phase is 0.25?, calculate the following: a.The frequency of the induced current in the rotor circuit at full load. b.The percentage...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT