Question

In: Electrical Engineering

A three phase transformer of 200MVA, 33kV/380kV, Yd11 is delivering nominal power at cosφ = 1....

A three phase transformer of 200MVA, 33kV/380kV, Yd11 is delivering nominal power at cosφ = 1.

  1. Calculate the nominal primary and secondary line current.
  2. Calculate the winding ratio n of this transformer.

The primary line current is 15,9A during an open circuit test. The measured power per phase is then 53kW. During a short circuit test (at nominal current), 271V primary line voltage is measured at cosφ = 0,225.

  1. Calculate the total iron losses and total copper losses of this transformer.
  2. Calculate the total iron losses if the transformer would be connected to 16,5kV (primary side).
  3. Draw the single-phase equivalent circuit of this transformer. Give also the phase quantities of the voltages and currents and indicate what the circuit elements represent.

Please show process and computations with comments.

Solutions

Expert Solution


Related Solutions

A three phase transformer of 400kVA, 10kV/400V, Dy11 is connected to its nominal load with cosφ...
A three phase transformer of 400kVA, 10kV/400V, Dy11 is connected to its nominal load with cosφ = 1. a) Calculate the nominal primary and secondary line current. b) Calculate the corresponding currents in the primary and secondary winding. At an open circuit test, the primary line current is 0,52A with cosφ = 0,05 at nominal line voltage. The short circuit test (at nominal current) shows 214V primary line voltage and P=1,333kW per phase. c) Calculate the total iron losses and...
The performance for a power factor of 1 of a 200KVA, 3000/380 V single phase transformer...
The performance for a power factor of 1 of a 200KVA, 3000/380 V single phase transformer is 0.98 for both full load and medium load. The vacuum power factor is 0.2 and the voltage drop at full load with a power factor of 0.8 is 4%. Determine the parameters of the equivalent circuit of the transformer referred to the primary side.
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
A synchronous generator is delivering 35% of the power that is capable of delivering to an...
A synchronous generator is delivering 35% of the power that is capable of delivering to an infinite bus. If the electrical power of the generator is doubled, determine the maximum value of rotor angle during the swinging of the generator around its new equilibrium position. Draw the corresponding power angle curve.
Determine the power efficiency of the transformer
Determine the power efficiency of the transformer
Generally, a single-phase power is commonly found in domestic households, whereas a three-phase power is preferable...
Generally, a single-phase power is commonly found in domestic households, whereas a three-phase power is preferable for larger demands. For safety purpose, over-current protection components are compulsory in the electrical distribution systems. i. Explain two advantages of a three-phase system compared to a single-phase system in the distribution system. ii. Briefly describe the characteristic and the function of two types over-current protection device installed in the distribution board (DB) residential building. iii. Miniature circuit breakers (MCB) with different current rating...
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100...
Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100 kVA with Zeq = 0.5 + j0.8 Ohm. If an autotransformer is built from this conventional transformer to supply a load at 2640V with supply voltage 2400V. Draw the autotransformer and calculate Zeq, the voltage, current and apparent power rating of the auto transformer. Also calculate the apparent power rating advantage of autotransformer over conventional transformer.
1. In a power system with negligible resistance, the three-phase fault current at a point is...
1. In a power system with negligible resistance, the three-phase fault current at a point is 8 pu. The series reactance to be inserted at the fault point to limit the short circuit current to 5 pu 2. A 3-phase, 15 MVA, 10 kV alternator has internal reactance of 6% and negligible resistance. Find the external reactance per phase to be connected in series with the alternator so that steady current on short circuit does not exceed 6 times the...
Similar conditions as in previous question. A simple 3-phase power system includes generator G, step-up transformer...
Similar conditions as in previous question. A simple 3-phase power system includes generator G, step-up transformer TX1, transmission line TL, step-down transformer TX2 and load L. All elements are rated for S = 50 MVA (3 phase). G: series impedance 0, rated voltage 600 V (line-to-line) TX1: series impedance ZTX1, voltage ratio 600 V : 100 kV (line-to-line) TL: series impedance ZTL; TX2: series impedance ZTX2; voltage ratio 100 kV : 1kV (line-to-line) L: impedance ZL. Per unit system is...
1. What is the type of transformer used in a SMPS power supply? Why is it...
1. What is the type of transformer used in a SMPS power supply? Why is it necessary to use such type of a transformer?