Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...

Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3 kV(rms). Find the total complex power delivered by the generator

Solutions

Expert Solution

Ans) Given load end line to neutral voltage is

We will first calculate complex power for each load

Load-1

The phase current is given as

Now 3 phase complex power of load 1 is

=============

Load-2

Delta connected phase voltage equals to line voltage i.e

line voltage leads phase voltage by 30 deg for balanced system

The phase current is given as

ow 3 phase complex power of load 2 is

===========

Load 3

Its complex power is given as

=======

Total KVA of load is given as

The total line current into the load is given as

The complex power in the distribution lines is given as

Now total complex power delivered by generator is given as


Related Solutions

A balanced Y-connected load having an impedance of 60 - j45Ω/ϕ is connected in parallel with...
A balanced Y-connected load having an impedance of 60 - j45Ω/ϕ is connected in parallel with a balanced Δ-connected load having an impedance of 90√2∠45∘ Ω/ϕ. The paralleled loads are fed from a line having an impedance of 2 + j2Ω/ϕ. The magnitude of the line-to-line voltage of the Δ-load is 200√3 V. Part A: Calculate the magnitude of the phase current in the Y-connected load. Part B: Calculate the magnitude of the phase current in the Δ-connected load. Part...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4 Ω per phase. The magnitude of the line current ILis:
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission...
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission line. The line-line voltage for the source is 100∟0° V/phase and the impedance of load is (27 + j18) Ω/phase. The transmission line has an impedance of (1 + j4) Ω/line. a) Draw the complete schematic of the power system showing the location of wattmeters. (Two-Wattmeter system is considered for this problem). Phase “a” could be considered as a reference phase. b) What must...
A three-phase balanced star load No. 1 of (120 +j90) ohms in parallel with another three-phase...
A three-phase balanced star load No. 1 of (120 +j90) ohms in parallel with another three-phase balanced star load No. 2 of (90 +j120) ohms, both are fed by three-phase balanced conductors of 3 ohms resistance and 4 ohms reactance. If the generator is 240 volts, with angle of -150° on phase c and reactance of 1 ohms, determine: a) the current on load N°1 on phase C, b) the terminal voltage of the generator on phase B, c) the...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The load impedances are Za = 14+j3 Ω , Zb = 5-j24Ω and Zc =1+j14 Ω  and the phase a line voltage has an effective value of 18 Kv: use line-to-neutral voltage of phase A as a reference. Find the line and neutral current, also find the reactive power delivered to load and power factor.
In a three-phase circuit the balanced delta load of (36 +j54) ohms is fed by impedance...
In a three-phase circuit the balanced delta load of (36 +j54) ohms is fed by impedance conductors (5 +j70) ohms. If the generator voltage is 120 V angle 0° phase A, calculate a) the bc voltage on the load, b) the powers in the conductors, c) the bc voltage of the delta load and d) the power delta on the load.
Question 5 a) Draw the circuit of a Three-phase bridge inverter using a Y-connected load and...
Question 5 a) Draw the circuit of a Three-phase bridge inverter using a Y-connected load and explain its operation using 180 degree conduction clearly showing the gating sequence and the corresponding output line voltages for each phase. (10) b) For the Y-connected load determine the line to neutral voltages for the three modes of operations. Draw the equivalent circuits for each mode and then draw the phase voltage waveforms for the 180-degree conduction. (7)
1) A load can be represented as a 1kOhm resistor. This impedance is subsequently connected to...
1) A load can be represented as a 1kOhm resistor. This impedance is subsequently connected to a sinusoidal 120V (rms) 60Hz voltage source. Find the current through the load both in phasor form and in time-domain form. Produce a well-labeled plot showing the voltage, the current and the power. a) A load can be represented as a 10μF capacitor connected in series with a 1kOhm resistor. This impedance is subsequently connected to a sinusoidal 120V (rms) 60Hz voltage source. Find...
b) The load connected to a three-phase supply comprises three similar coils connected in star. If...
b) The load connected to a three-phase supply comprises three similar coils connected in star. If the phase currents are 10A and the total active power and power factor absorb by the loads are 3kW and 0.8 lagging, respectively. Find: i. The magnitude of phase and line voltages ii. Total apparent power (1 mark) iii. The impedance of each coil. c) If the coil in Q3(b) are now connected in delta to the same three-phase supply, calculate the magnitude of...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed of 1750rpm. The rotational mechanical losses are constant and equal to 500W. The core losses are constant and equal to 300W. The copper losses in the stator equal to the copper losses in the rotor at full load. If the rotor resistance per phase is 0.25?, calculate the following: a.The frequency of the induced current in the rotor circuit at full load. b.The percentage...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT