Question

In: Electrical Engineering

Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100...

Problem 3: A single phase 60 Hz two-winding power transformer is rated at 2400V/240V and 100 kVA with
Zeq = 0.5 + j0.8 Ohm. If an autotransformer is built from this conventional transformer to supply a load at
2640V with supply voltage 2400V. Draw the autotransformer and calculate Zeq, the voltage, current and
apparent power rating of the auto transformer. Also calculate the apparent power rating advantage of
autotransformer over conventional transformer.

Solutions

Expert Solution

Advantages of using Auto Transformers

  1. For transformation ratio = 2, the size of the auto transformer would be approximately 50% of the corresponding size of two winding transformer. For transformation ratio say 20 however the size would be 95 %. The saving in cost of the material is of course not in the same proportion. The saving of cost is appreciable when the ratio of transformer is low, that is lower than 2. Thus auto transformer is smaller in size and cheaper.
  2. An auto transformer has higher efficiency than two winding transformer. This is because of less ohmic loss and core loss due to reduction of transformer material.
  3. Auto transformer has better voltage regulation as voltage drop in resistance and reactance of the single winding is less.

Related Solutions

A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
A single-phase 300-kVA, 220/4400 V, 60 Hz transformer yielded the following information when tested: High voltage...
A single-phase 300-kVA, 220/4400 V, 60 Hz transformer yielded the following information when tested: High voltage winding open: Voltage=220 V, Current=40 A Power=l 000W Low voltage terminal shorted: Voltage= 195 V, Current=68.18A Power=4000W Find the equivalent circuit of the transformer as viewed from the high voltage Calculate the .efficiency of the transformer when it delivers its rated load at rated terminal voltage and 8 power factor lagging.
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding...
A 3-phase, 5 kVA, 208 V, four-pole, 60 Hz, Y-connected synchronous machine has negligible stator winding resistance and a synchronous reactance of 8 per phase at rated terminal voltage. Themachine is operated as a generator and delivers rated kVA at 0.8 power factor lagging. (a) Determine the excitation voltage, (b) Find the power angle, (c) Draw the phasor diagram, (d) Find the stator current assuming that the field excitation current is now increased by 20 % (without changing the prime...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A single-phase transformer 5 kVA, operating at 50 Hz frequency has turns ratio of 20. The...
A single-phase transformer 5 kVA, operating at 50 Hz frequency has turns ratio of 20. The primary and the secondary winding resistances are 0.15 Ω and 0.025 Ω respectively, and the primary and secondary leakage reactances are 0.65 Ω and 0.15 Ω respectively. The magnetizing inductance and core loss resistance are 6 Ω and 1 Ω respectively. i. Calculate the primary and secondary impedances referred to primary and sketch the APPROXIMATE equivalent circuit. (Note: please show all parameters in the...
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and...
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and connected as Y its neutral is kept floating. It is directly tied to three loads, one consuming 50% of its capacity, and each of the other two consuming 25% of its capacity. A three-phase to ground fault could occur at any of the loads. Draw a one-line diagram of this system, then describe what type of faults could occur in the generator and diesel...
The performance for a power factor of 1 of a 200KVA, 3000/380 V single phase transformer...
The performance for a power factor of 1 of a 200KVA, 3000/380 V single phase transformer is 0.98 for both full load and medium load. The vacuum power factor is 0.2 and the voltage drop at full load with a power factor of 0.8 is 4%. Determine the parameters of the equivalent circuit of the transformer referred to the primary side.
The 500 KVA, 69kV/11kV, 60 Hz transformer has total resistance Rp of 100 Ω and total...
The 500 KVA, 69kV/11kV, 60 Hz transformer has total resistance Rp of 100 Ω and total leakage reactance of Xp of 600 Ω. Calculate The per unit impedance of the transformer in percent (just magnitude) The voltage regulation of the transformer when it delivers 200 KVA with a lagging power factor of 90% while the secondary voltage is fixed at 11 kV. The actual primary voltage V1. The actual line current I1.
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage...
A single phase, 300???, 11??/2.2??, 60 ?? transformer has the following parameters referred to the high-voltage side: ?? = 57.6??, ?? = 16.34??, ??? = 2.784? and ??? = 3.5?. If a load of ????? = 16∠30°? connected to the low-voltage side: a) Find the voltage regulation? b) Draw the phasor diagram? c) Find the efficiency of the transformer? d) Repeat part a and b at ????? = 16∠ − 30°??