In: Electrical Engineering
345 kV, 50 Hz, 3-phase transmission line is 100 km long. The resistance is 0.048 Ω/km and the inductance is 1,24 mH/km. The shunt capacitance is 0.0174 μF/km. The receiving end load is 216 MW with 0.8 power factor lagging at 325 kV.
(a) Compute ABCD parameters using π equivalent circuit
(b) Sending end voltage VS,
(c) Sending end current IS,
(d) Efficiency
(a) A=0.989 ; B=39.1 ohm ; C= j0.000544 Siemens D=0.989 (only magnitude mentioned)
(b) Vs=344.75 kV ; (c) Is=421.23 amp
(d) efficiency =95.22%