Question

In: Electrical Engineering

345 kV, 50 Hz, 3-phase transmission line is 100 km long. The resistance is 0.048 Ω/km...

345 kV, 50 Hz, 3-phase transmission line is 100 km long. The resistance is 0.048 Ω/km and the inductance is 1,24 mH/km. The shunt capacitance is 0.0174 μF/km. The receiving end load is 216 MW with 0.8 power factor lagging at 325 kV.

(a) Compute ABCD parameters using π equivalent circuit

(b) Sending end voltage VS,

(c) Sending end current IS,

(d) Efficiency

Solutions

Expert Solution


(a) A=0.989 ; B=39.1 ohm ; C= j0.000544 Siemens D=0.989 (only magnitude mentioned)

(b) Vs=344.75 kV ; (c) Is=421.23 amp

(d) efficiency =95.22%


Related Solutions

A three-phase 60-Hz transmission line is energized with 420 kV at the sending end. This line...
A three-phase 60-Hz transmission line is energized with 420 kV at the sending end. This line is lossless and 400 km long with ? = 0.001265 rad/km and ?? = 260 Ω. a) Suppose a three-phase short-circuit occurs at the receiving end. Determine the receiving end current and the sending end current. b) Determine the reactance and MVar of a shunt reactor to be installed at the load bus to limit the no-load receiving-end voltage to 440 kV. c) When...
A 3-phase line has a resistance of 9 Ω/phase and a reactance of 23 Ω/phase. The...
A 3-phase line has a resistance of 9 Ω/phase and a reactance of 23 Ω/phase. The load at the receiving end is 130 MW at 0.8 p. f. lagging. Find the capacity of the synchronous condenser required to be connected at the receiving end to maintain the voltage at both ends of the transmission line at 132 KV.
The impedance of a three-phase, 50 km long power transmission line per unit length is 0.05...
The impedance of a three-phase, 50 km long power transmission line per unit length is 0.05 + j0.1  / km. A load with a power coefficient of 0.8 forward is fed from the end of the line. Line and end of line of energy transmission line According to the intention to keep the voltage between phases constant at 154 kV; a) Active and reactive power values ​​drawn from the beginning and end of the line, b) Calculate the lost...
(a) A steel power transmission line has a resistance of 0.0430 Ω/km. What is its mass...
(a) A steel power transmission line has a resistance of 0.0430 Ω/km. What is its mass per kilometer (in kg/km)? (Assume the density of steel is 7.8 ✕ 103 kg/m3.)   ________ kg/km (b) What is the mass per kilometer (in kg/km) of an iron line having the same resistance? (Assume the density of iron is 7.8 ✕ 103 kg/m3.) _______ kg/km
Find the main dimensions of a 2500 KVA, 187.5 rpm, 50 Hz, 3 phase, 3 kV,...
Find the main dimensions of a 2500 KVA, 187.5 rpm, 50 Hz, 3 phase, 3 kV, salient pole synchronous generator. The generator is to be a vertical, water wheel type. The specific magnitude loading is 0.6 Wb/m2 and the specific electric loading is 34000 A/m. Use circular pole with ratio of core length to pole pitch=0.65. Find the normal speed.
A 35 km, 34.5-kV, 60-Hz three phase line has a positive-sequence series impedance z = 0.10...
A 35 km, 34.5-kV, 60-Hz three phase line has a positive-sequence series impedance z = 0.10 + j0.40 Ohms/km. The load at the receiving end absorbs 15 MVA at 33 kV. Assuming a short line, calculate: (a) the ABCD parameters, (b) the sending-end voltage for a load power factor of 0.95 lagging, (c) the sending-end voltage for the a load power factor of 0.9 leading. (d) For which case is the sending-end voltage higher?
A 60-Hz, 230-km, three phase overhead transmission line has a series impedance z = 0.85<78.04 ̊...
A 60-Hz, 230-km, three phase overhead transmission line has a series impedance z = 0.85<78.04 ̊ /km and a shunt admittance y = 5.105 x 10-6 < 90 ̊ S/km. The load at the receiving end is 135 MW at unity power factor and 215 kV. Determine the voltage, current, real and reactive power at the sending end and the percent voltage regulation of the line.
A 3-phase 60 HZ , 200km transmission line has a series impedance of z= 0.10 +...
A 3-phase 60 HZ , 200km transmission line has a series impedance of z= 0.10 + j0.35 Ω/km and a capacitive reactance of 0.2 x 10 6 Ω-km. At the receiving end, the line delivers 250 MW @230/30θ kV and 0.95 lagging power factor. Determine a) The line impedance and shunt admittance b) The A, B, C , D parameters c) Sending end complex power and power factor d) Is the PF is leading or lagging e) Voltage regulation for...
For 345 KV, a three conductor per phase are to be used at 0.30 meters per...
For 345 KV, a three conductor per phase are to be used at 0.30 meters per conductor in a flat horizontal layout. The distance between the centers of each bundle is 4 meters in a delta configuration. GMR for the conductors is 0.012 m Find: GMD, L, and XL
A lossless 50-Ω transmission line is terminated in a load with Z L = (35 −...
A lossless 50-Ω transmission line is terminated in a load with Z L = (35 − j47.5) Ω using a short circuited stub. Use the Smith chart to determine position and length line for the stub? show step by step by hand and draw by hand I want details so I can understand
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT