Question

In: Electrical Engineering

Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with...

Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with a 50-Hz, 50-kVA, star-star transformer bank of vector group Yy0. Both have a bank ratio of 2000/200-V. The equivalent impedances referred to the respective secondaries are ZΔ = 0.1106/60.2° Ω and ZY = 0.0369/60.2° Ω. (a) Assuming the load switch to be open, draw the connection diagram   (3.0 marks). (b) Determine the magnitude of the current circulating in each transformer secondary   (15.0 marks). (c) Express the current in (b) as a percent of the rated transformer current for each transformer   (2.0 marks).                                                                                  Use the method of mesh analysis applied to the three-phase circuits (marks will not be awarded for using the single-phase equivalent method). show all your steps

Solutions

Expert Solution


Related Solutions

A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of...
A single-phase transformer of 3 kVA, 60 Hz, has a voltage ratio on open circuit of 240 / 120 V. The primary and secondary resistances are 0.25 Ω and 0.05 Ω respectively, the corresponding leakage reactance being 0.75 Ω and 0.18 Ω. The transformer delivers current to the load at a 0.9 power factor lagging. Determine the voltage across the load.                                                                   Determine the power dissipated by the load.                                                          Determine percentage voltage regulation referred to the secondary...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are...
4.11)The equivalent circuit parameters of a 150 kVA, 2400 V/ 240 V, 60 Hz transformer are as follows: RHV = 0.21Ω, RLV = 2mΩ, XlHV = 0.45Ω, XlLV = 4.6mΩ, XmHV = 1.6kΩ, and RcHV = 12kΩ. The transformer delivers to a load, rated current at a power factor of 0.85 lagging at rated voltage. Determine the input voltage, current, apparent power and power factor, (a) using the approximate equivalent circuit, and (b) not using the approximate equivalent circuit. Problem...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of...
A 350-KVA 2300  230; volt, 60-hz transformer has percent core loss, resistance and percent leakage reactance of 0.56 , 33 and 5.57 respectively. For 10 degree increments of power-factor angle, tabulate and plot percent regulation, and efficiency. Power factor for operation between 0.5 lagging and 0.5 leading.
Find the main dimensions of a 2500 KVA, 187.5 rpm, 50 Hz, 3 phase, 3 kV,...
Find the main dimensions of a 2500 KVA, 187.5 rpm, 50 Hz, 3 phase, 3 kV, salient pole synchronous generator. The generator is to be a vertical, water wheel type. The specific magnitude loading is 0.6 Wb/m2 and the specific electric loading is 34000 A/m. Use circular pole with ratio of core length to pole pitch=0.65. Find the normal speed.
A 20MVA, 11kV/132 kV, star-delta transformer is being protected by a biased differential protection system. The...
A 20MVA, 11kV/132 kV, star-delta transformer is being protected by a biased differential protection system. The transformer is supplied from 132 kV grids and on full load operation. Determine the suitable CTs ratio at both side of the transformer if current at restraints coil is rated at 5 A. (CT ratios available: 100/5A, 300/5A, 600/5A, 800/5A, 900/5A, 1000/5A, 1500/5A, 2000/5A, 3000/5A) If lightning strikes at the secondary of the transformer which injecting IL=10kA to the system; (i) Determine the primary...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is adjustable from no load to 120 percent rated KVA. The percent resistance, percent reactance, and percent core loss are m+1.56, m+3.16, and m+0.42 respectively. For 2 KVA increments of load, tabulate and plot the efficiency of the transformer from no load to 120 percent rated load. Use Matlab n=20 m=.2
Assume that you have a clock signal with frequency of 50 Hz, and you want to...
Assume that you have a clock signal with frequency of 50 Hz, and you want to divide this signal into a frequency of 1 Hz signal. The counter chips you must use are synchronous decade (MOD 10) counter chips 74160 and synchronous MOD 16 counter chips 74161. Please use the back side of this paper to draw your circuit diagram with all the details. You can use counter frequency division method to step down a higher frequency signal to a...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The following results were obtained from open circuit (no-load) and short circuit tests.             Open Circuit (no-load) Test Applied Stator Voltage VLine (V) Stator Line Current ILine (A) Total Input Power Pin (W) 240 9.6 536 220 7.2 420 200 5.4 352 180 4.3 304 160 3.5 276 140 3.0 248 120 2.5 224             Short Circuit (locked rotor) Test Applied Stator Voltage VLine (V) Stator Line...