Question

In: Electrical Engineering

A balanced Y-connected load having an impedance of 60 - j45Ω/ϕ is connected in parallel with...

A balanced Y-connected load having an impedance of 60 - j45Ω/ϕ is connected in parallel with a balanced Δ-connected load having an impedance of 90√2∠45∘ Ω/ϕ. The paralleled loads are fed from a line having an impedance of 2 + j2Ω/ϕ. The magnitude of the line-to-line voltage of the Δ-load is 200√3 V.

Part A: Calculate the magnitude of the phase current in the Y-connected load.

Part B: Calculate the magnitude of the phase current in the Δ-connected load.

Part C: Calculate the magnitude of the current in the line feeding the loads.

Part D: Calculate the magnitude of the line voltage at the sending end of the line.

Solutions

Expert Solution


Related Solutions

Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4...
A balanced three-phase generator delivers 6.3 kW to a delta-connected load with impedance 13 - j23.4 Ω per phase. The magnitude of the line current ILis:
1) A load can be represented as a 1kOhm resistor. This impedance is subsequently connected to...
1) A load can be represented as a 1kOhm resistor. This impedance is subsequently connected to a sinusoidal 120V (rms) 60Hz voltage source. Find the current through the load both in phasor form and in time-domain form. Produce a well-labeled plot showing the voltage, the current and the power. a) A load can be represented as a 10μF capacitor connected in series with a 1kOhm resistor. This impedance is subsequently connected to a sinusoidal 120V (rms) 60Hz voltage source. Find...
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission...
A balanced three-phase delta-connected load is connected to a balanced three-phase delta-connected source via a transmission line. The line-line voltage for the source is 100∟0° V/phase and the impedance of load is (27 + j18) Ω/phase. The transmission line has an impedance of (1 + j4) Ω/line. a) Draw the complete schematic of the power system showing the location of wattmeters. (Two-Wattmeter system is considered for this problem). Phase “a” could be considered as a reference phase. b) What must...
In a three-phase circuit the balanced delta load of (36 +j54) ohms is fed by impedance...
In a three-phase circuit the balanced delta load of (36 +j54) ohms is fed by impedance conductors (5 +j70) ohms. If the generator voltage is 120 V angle 0° phase A, calculate a) the bc voltage on the load, b) the powers in the conductors, c) the bc voltage of the delta load and d) the power delta on the load.
6.9 A3 ϕ, 11 kV, 60 Hz, 25 MVA, Y-connected cylindrical-rotor synchronous machine generator has Ra...
6.9 A3 ϕ, 11 kV, 60 Hz, 25 MVA, Y-connected cylindrical-rotor synchronous machine generator has Ra = 0.45 Ω per phase and Xs = 4.5 Ω per phase. The generator delivers the rated load at 11 kV and 0.85 lagging power factor. Determine the excitation voltage, Ef, for this operating condition. 6.11 The synchronous machine in Problem 6.9 is operated as a synchronous motor and it is drawing rated MVA at 0.85 lagging power factor. Determine the excitation voltage, Ef,...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The...
An unbalanced three-phase wye-connected and grounded load is connected to a balanced three-phase four-wire source. The load impedances are Za = 14+j3 Ω , Zb = 5-j24Ω and Zc =1+j14 Ω  and the phase a line voltage has an effective value of 18 Kv: use line-to-neutral voltage of phase A as a reference. Find the line and neutral current, also find the reactive power delivered to load and power factor.
A delta connected load has a parallel combination of resistance 5Ω and capacitive reactance –j5Ω in...
A delta connected load has a parallel combination of resistance 5Ω and capacitive reactance –j5Ω in each phase. If a balanced three phase 400V supply is applied between lines, find the phase currents and line currents and draw the phasor diagram
A lossless transmission line of length l=0.4? is terminated with a complex load impedance Z_L=60+j50 ?...
A lossless transmission line of length l=0.4? is terminated with a complex load impedance Z_L=60+j50 ? and characteristic impedance (Z_0=50 ?). Use Smith Chart to find: The VSWR on the line; The reflection coefficient at the load and its phase angle; The load admittance of the line Y_L in S; The input impedance of the line in ?; The distance to the first voltage minimum from the load in ?; and The distance to the first voltage maximum from the...
AC Thevenin has an impedance of Zt = 6 + j75 What is the load impedance...
AC Thevenin has an impedance of Zt = 6 + j75 What is the load impedance for MPT? If a resistor was connected as load, what would the R value need to be for MPT?
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT