Question

In: Electrical Engineering

A 20MVA, 11kV/132 kV, star-delta transformer is being protected by a biased differential protection system. The...

A 20MVA, 11kV/132 kV, star-delta transformer is being protected by a biased differential protection
system. The transformer is supplied from 132 kV grids and on full load operation. Determine the
suitable CTs ratio at both side of the transformer if current at restraints coil is rated at 5 A. (CT ratios
available: 100/5A, 300/5A, 600/5A, 800/5A, 900/5A, 1000/5A, 1500/5A, 2000/5A, 3000/5A) If
lightning strikes at the secondary of the transformer which injecting IL=10kA to the system;

(i) Determine the primary current, Ip and secondary current, Is for the 20MVA transformer at the CTs’
output. Ignore the impedance of the cables.
(ii) Determine the average restraint current and operating current in the relay.
(iii) The bias characteristic of the relay is y = mx + c where y is the operating current, x is the
average restraint current and m is slope. Draw a neat sketch of the characteristic curve of this
relay if relay setting IS = 0.2A and percentage bias setting is set to 25%. Clearly mark the scales
used for both the x-axis and y-axis neatly on the sketch.
(iv) Mark the operating point of the relay due to this fault on the sketch. Will the relay operate? If
yes, give your explanation.

Solutions

Expert Solution


Related Solutions

what is the used of The HFCT and its located cable of the transformer 132 KV...
what is the used of The HFCT and its located cable of the transformer 132 KV Cables (PD) ? and how its work
A 100MVA, 400 delta / 11Y kV, 3-phase transformer has Z(eq) = 0.02+j0.05 ohm per phase...
A 100MVA, 400 delta / 11Y kV, 3-phase transformer has Z(eq) = 0.02+j0.05 ohm per phase referred to the low-voltage side, and R(c) = 1800 ohm per phase referred to the high-voltage side. If the transformer supplies rated voltage at full load at 0.8 power factor lagging. Determine its voltage regulation and efficiency.
Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with...
Assume that a 50-Hz, 50-kVA, star-delta transformer bank of vector group Yd11 is accidentally paralleled with a 50-Hz, 50-kVA, star-star transformer bank of vector group Yy0. Both have a bank ratio of 2000/200-V. The equivalent impedances referred to the respective secondaries are ZΔ = 0.1106/60.2° Ω and ZY = 0.0369/60.2° Ω. (a) Assuming the load switch to be open, draw the connection diagram   (3.0 marks). (b) Determine the magnitude of the current circulating in each transformer secondary   (15.0 marks). (c)...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT