In: Mechanical Engineering
A refrigeration cycle absorbs 20,000 kJ/h of heat from a space
maintained at -45oC and rejects heat to the surrounding
air at 30oC.
i. Determine the actual power input to the refrigeration cycle if
the coefficient of performance (COP) of the refrigeration cycle is
25% of that of a reversible refrigerating cycle operating between
the same two temperature reservoirs (kW).
ii. Determine the minimum work input to the refrigeration cycle
(kW).
iii. Will the heat rejected to the surrounding by the actual
refrigeration be greater, smaller or the same as the heat rejected
to the surrounding by the reversible refrigeration cycle?
Ans
(i) For reversible refrigerating cycle, (COP)rev. = T2 / (T1 -T2)
= 228 / (303 - 228)
= 3.04
For actual cycle, (COP)actual = 25% of (COP)rev.
= 0.25 * 3.04
= 0.76
Also, (COP)actual = Q2 / W
0.76 = 20000 / W
W = 26315.79 kJ/h
= ( 26315.79 / 3600) kW
= 7.31 kW (ans)
where, 'W' is the actual power input
(ii) Work input will be minimum in case of refrigeration cycle, therefore,
(COP)rev. = Q2 / Wmin
3.04 = 20000 / Wmin
Wmin = 6578.95 kJ/h
= (6578.95 / 3600) kW
= 1.83 kW (ans)
(iii) Heat rejected by a actual refrigeration cycle is always greater than the reversible refrigeration cycle. We can show this as follows
Heat rejected by actual refrigeration cycle, (Q2)actual = Q1 + W
= 20000 + 26315.79
= 46315.79 kJ/h
Heat rejected by reversiblel refrigeration cycle, (Q2)rev = Q1 + Wrev
= 20000 + 6578.95
= 26578.95 kJ/h
So, we see that (Q2)actual > (Q2)rev