QUESTION 5:
A) Given that Van = 230 ̶ 10o for positive sequence voltage Y connection load, Find the phase voltages and line voltages then draw a phasor diagram to show all voltages.
B) Consider a 300 kVA single phase load with pf = 0.85 lagging and it is required to correct the pf to 0.90 leading, Find the reactive power (Qc) added after using the parallel capacitors and the value of capacitor added if V = 380 kV and f = 50 Hz.
Solution :
A ) The solution is attached below
B) Let the true power be P Watts
and Apparent power (Given) S = 300 KVA
Given p.f.1 = 0.85 lagging
p.f.2 = 0.90 lagging
f = 50 Hz
V = 380 KV
To find QC and the value of capacitor added for power factor correction.
Power Factor = True power / apparent Power
=> p.f.1 = True power (P)/Apparent power(S)
=> 0.85 = P(W)/(300*1000)(VA) {1000 is multiplied to convert KVA into VA}
=> P = 0.85 * 300 *1000 (W)
=> P = 255000 W or 255 KW
Now as
p.f.1 = 0.85 lag = => = 31.788
p.f.2 = 0.90 lag = => = 25.841
The required capacitor KVAR i.e. QC to improve the power factor will be
Qc
=> Qc = 255 (tan(31.788)- tan(25.841))
=> Qc = 34.535 KVAR
i.e. reactive power Qc added after parallel capacitor addition is 34.535 KVAR
now the value of capaciotr required C will be calculated by the formula
QC = 2 * pi * f * C* V^2
34.535 = 2 *3.14 *50 *C *380 * 380
=> C = 0.7616 microfarad,