Explain why the positive sequence impedance of a transmission line and transformer is the same as...

Explain why the positive sequence impedance of a transmission line and transformer is the same as the negative sequence impedance but is different from the zero sequence impedance.

Solutions

Expert Solution

The impedance offered by the system to the flow of positive sequence current is called Positive sequence impedance

The impedance offered by the system to the flow of negative sequence current is called Negative sequence impedance

The impedance offered by the system to the flow of zero sequence current is known as Zero sequence impedance

The sequence impedance varies with the type of power system components under consideration :-

1) In static and balanced power system components like transformer and lines, the sequence impedance offered by the system are the same for positive and negative sequence currents.In other words, the positive sequence impedance and negative sequence impedance are same for transformers and power lines

2) But in case of rotating machines the positive and negative sequence impedance are different

3) The assignment of zero sequence impedance values is more complex one. This is because the three zero sequence current at any point in a electrical power system, being in phase, do not sum to zero but must return through the neutral and /or earth.In three phase transformer and machine fluxes due to zero sequence components do not sum to zero in the yolk.


Related Solutions

The positive-sequence line impedance as well as CT and VT ratios at B1 for the 33...
The positive-sequence line impedance as well as CT and VT ratios at B1 for the 33 kV system as shown in Table 1 and Table 2 below : Table 1 Line Positive Sequence Impedance 1-2 4+j30 2-3 4+j40 3-4 4+j50 Table 2 Breaker CT Ratio VT Ratio B1 100/5 A 33000/5 V Zone 1 reaches 90% of the protected line while zone 2 extend beyond the protected line up to 50% of the adjacent line and Zone 3 covers the...
Derive aformula for the input impedance of a terminated lossless transmission line.
Derive aformula for the input impedance of a terminated lossless transmission line.
Assuming that the length of a lossless transmission line with the normalized load impedance of zL...
Assuming that the length of a lossless transmission line with the normalized load impedance of zL = ZL/Z0 = 1 + j1 is l = 2.25λz , there are a total of (A) 2 voltage maxima and 2 voltage minima (B) 2 voltage maxima and 3 voltage minima (C) 3 voltage maxima and 2 voltage minima (D) 4 voltage maxima and 4 voltage minima (E) 4 voltage maxima and 5 voltage minima (F) 5 voltage maxima and 4 voltage minima...
An input transmission line of characteristic impedance Z01 splits off into three identical output transmission lines...
An input transmission line of characteristic impedance Z01 splits off into three identical output transmission lines having characteristic impedance Z02 = 3Z01. This represents a four-port system. Find all 16 of the S parameters for this system. Note: Many of the 16 Sij parameters will be identical. There should be only four values that are distinct. SHOW WORK!!
12. At a frequency of 80 MHz, a lossless transmission line has a characteristic impedance of...
12. At a frequency of 80 MHz, a lossless transmission line has a characteristic impedance of 300Ω and a wavelength of 2.5m. (a) Find L; (b) Find C. (c) If the line is terminated with the parallel combination of 200Ω and 5 pF, determine Γ and SWR.
A 35 km, 34.5-kV, 60-Hz three phase line has a positive-sequence series impedance z = 0.10...
A 35 km, 34.5-kV, 60-Hz three phase line has a positive-sequence series impedance z = 0.10 + j0.40 Ohms/km. The load at the receiving end absorbs 15 MVA at 33 kV. Assuming a short line, calculate: (a) the ABCD parameters, (b) the sending-end voltage for a load power factor of 0.95 lagging, (c) the sending-end voltage for the a load power factor of 0.9 leading. (d) For which case is the sending-end voltage higher?
A 3-phase 60 HZ , 200km transmission line has a series impedance of z= 0.10 +...
A 3-phase 60 HZ , 200km transmission line has a series impedance of z= 0.10 + j0.35 Ω/km and a capacitive reactance of 0.2 x 10 6 Ω-km. At the receiving end, the line delivers 250 MW @230/30θ kV and 0.95 lagging power factor. Determine a) The line impedance and shunt admittance b) The A, B, C , D parameters c) Sending end complex power and power factor d) Is the PF is leading or lagging e) Voltage regulation for...
A lossless transmission line of length l=0.4? is terminated with a complex load impedance Z_L=60+j50 ?...
A lossless transmission line of length l=0.4? is terminated with a complex load impedance Z_L=60+j50 ? and characteristic impedance (Z_0=50 ?). Use Smith Chart to find: The VSWR on the line; The reflection coefficient at the load and its phase angle; The load admittance of the line Y_L in S; The input impedance of the line in ?; The distance to the first voltage minimum from the load in ?; and The distance to the first voltage maximum from the...
The impedance of a three-phase, 50 km long power transmission line per unit length is 0.05...
The impedance of a three-phase, 50 km long power transmission line per unit length is 0.05 + j0.1  / km. A load with a power coefficient of 0.8 forward is fed from the end of the line. Line and end of line of energy transmission line According to the intention to keep the voltage between phases constant at 154 kV; a) Active and reactive power values ​​drawn from the beginning and end of the line, b) Calculate the lost...
A 60-Hz, 230-km, three phase overhead transmission line has a series impedance z = 0.85<78.04 ̊...
A 60-Hz, 230-km, three phase overhead transmission line has a series impedance z = 0.85<78.04 ̊ /km and a shunt admittance y = 5.105 x 10-6 < 90 ̊ S/km. The load at the receiving end is 135 MW at unity power factor and 215 kV. Determine the voltage, current, real and reactive power at the sending end and the percent voltage regulation of the line.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT