In: Electrical Engineering
The positive-sequence line impedance as well as CT and VT ratios at B1 for the 33 kV system as shown in Table 1 and Table 2 below :
Table 1
Line | Positive Sequence Impedance |
1-2 | 4+j30 |
2-3 | 4+j40 |
3-4 | 4+j50 |
Table 2
Breaker | CT Ratio | VT Ratio |
B1 | 100/5 A | 33000/5 V |
Zone 1 reaches 90% of the protected line while zone 2 extend beyond the protected line up to 50% of the adjacent line and Zone 3 covers the protected line up to 25%. Determine the settings Zr1, Zr2 and Zr3 for the B1 three-zone, directional impedance relays. Draw its MHO relay diagram and impedance relay diagram.
Transmission line impedence transferred to relay side is given as
So,
The impedence relays setting of B1 is following,
The impedence relay diagram is shown in followin figure in which Z1, Z2, Z3 represents the zone 1,2,and 3 protection impedence setting
For Mho Relay,
here MTA(Maximum Torque Axis is not provided so taken as 90 degree.
So,
Similarly,
The mho diagram is drawn following.