Question

In: Finance

A standard electric motor is rated at 10 horsepower (HP) and costs $800. Its fullload efficiency...

A standard electric motor is rated at 10 horsepower (HP) and costs $800. Its fullload

efficiency is specified to be 92%. A newly designed, high efficiency motor of

the same size has an efficiency of 95%, but costs $1,200. It is estimated that the

motors will operate at a rated 10-HP output for 2,000 hours a year, and the cost of

energy will be $0.07 per kilowatt-hour. Each motor is expected to have 12-year

life. At the end of 12 years, the first motor will have a salvage value of $50, and

the second motor will have a salvage value of $100. Consider the MARR to be

8%. (Note: 1HP = 0.7457 KW)

What is the net present value (NPW) of the cash flows associated with the high

efficiency motor?

Solutions

Expert Solution

Step 1 : Identification of Alternatives

Alternative 1 Standard Motor

Alternative 2 High Efficiency Motor

Step 2: Table showing Data for Both the Machines

Particulars Standard Motor High Efficiency Motor
Efficiency 92% 95%
Cost $800.00 $1,200.00
Operating Hours 2000 2000
Cost of Energy Per KWH $0.07 $0.07
Life 12 12
Salvage $50.00 $100.00
Interest Rate 8% 8%

Step3 : Required NPV of New Efficient Machine

NPV= Present Value of Cash Inflows - Present Value of Cash Outflows

Calculation of NPV

Particulars High Efficiency Motor Period PVF @8% Present Value
Cash Outflows
Cost of Motor $(1,200.00) 0 1 $(1,200.00)
Cash Inflows
Annual Revenue (Note 1) $991.78 1-12 7.536 $7,474.06
Salvage Value   $100.00 12 0.397 $39.70
NPV $6,313.76

NPV of New Efficiency Motor is $6313.76

Notes

1. Calculation of Cash Flows from New Efficient Machine

Particulars High Efficiency Motor
Cash Outflows
Cost of Motor $(1,200.00)
Cash Inflows
Efficiency 95%
Operating Hours 2000
Output In HP 19000
Output in KW (units) (A) 14168.3
Cost of Energy Per KWH (B) $0.07
Revenue/ Cash Inflows (A)x(B) $ 991.78
Salvage at the end of Yr 12 $100.00



Related Solutions

A standard electric motor is rated at 10 horsepower (HP) and costs $800. Its fullload efficiency...
A standard electric motor is rated at 10 horsepower (HP) and costs $800. Its fullload efficiency is specified to be 87%. A newly designed, high efficiency motor of the same size has an efficiency of 93%, but costs $1,200. It is estimated that the motors will operate at a rated 10-HP output for 2,500 hours a year, and the cost of energy will be $0.07 per kilowatt-hour. Each motor is expected to have 12-year life. At the end of 12...
A special-purpose 30-horsepower electric motor has an efficiency of 90 %. Its purchase and installation price...
A special-purpose 30-horsepower electric motor has an efficiency of 90 %. Its purchase and installation price is $2 200. A second 30-horsepower high-efficiency motor can be purchased for $3 200 , and its efficiency is 93 %. Either motor will be operated 4 000 hours per year at full load, and electricity costs $0.10 per kilowatt-hour (kWh). MARRequals15 % per year, and neither motor will have a market value at the end of the eight-year study period. Most motors are...
a water pumping company wants to purchase an electric motor rated at 15 Hp for 1000$(...
a water pumping company wants to purchase an electric motor rated at 15 Hp for 1000$( 1 HP= 0.7457kw ). the service life of motor is known to be 10 years with negligible salvage value.its full load efficiency is 85%. the cost of energy is 0.08$ per kWhr. the intended of the motor is 4000 hours per year .Determine the present worth for the total cost of owning and operating the motor at 10% interest rate A-19,695 $ B- 26,875...
Problem: A PM DC motor has the following parameters: Rated Power 10 hp; Rated armature voltage...
Problem: A PM DC motor has the following parameters: Rated Power 10 hp; Rated armature voltage 230 V-DC; Rated RPM: 1800; Armature Resistance: 0.2 Ohm Armature Inductance: 0.005 H Inertia (motor plus mechanical load): 0.1 kgm^2; Viscous friction coefficient: 0.015 Nms 1. Compute the voltage constant of the motor. Also compute the rated current and rated torque of the motor (obtained at the rated RPM). If the motor is supplied by 230 V across the armature, and the only torque...
1. three-phase induction motor rated 250 hp, 0.7 pf and 80% efficiency. Determine the minimum size...
1. three-phase induction motor rated 250 hp, 0.7 pf and 80% efficiency. Determine the minimum size in kVAR of a capacitor needed to prevent overloading the transformers.Two single-phase transformers each rated 150 kVA are connected open delta supplying a 2. A 2.2 kV, 200 hp, delta- connected, 3 phase synchronous motor is operating on full load at an efficiency of 0.88 and pf of 0.8 leading. The armature has a reactance per phase of 5 ohms and negligible resistance. Solve...
A manufacturing company is considering purchasing a 10 HP electric motor which it estimates will run...
A manufacturing company is considering purchasing a 10 HP electric motor which it estimates will run an average of 6 hours per day for 250 days per year. Past experience indicates that: (1) its annual cost for taxes and insurance averages 2.5% of first cost, (2) it must make 10% on invested capital before income tax considerations, and (3) it must recover capital invested in machinery within 5 years. Two motors are offered to the company. Motor A costs $...
3. Consider the investment project given in the below table: An electric motor is rated at...
3. Consider the investment project given in the below table: An electric motor is rated at 10 horsepower (HP) and costs $1,200. Its full-load efficiency is specified to be 85%. A newly designed high-efficiency motor of the same size has an efficiency of 90%, but it costs $1,600. It is estimated that the motors will operate at a rated 10 HP output for 2,000 hours/year, and the cost of energy will be $0.09/kilowatt- hour. Each motor is expected to have...
a three-phase bipolar motor of 10.72 [HP] has an efficiency of 80% when working at full...
a three-phase bipolar motor of 10.72 [HP] has an efficiency of 80% when working at full load at 2700 (rpm), if it is connected to a network of 440 (V) at 50 [Hz] calculate a.) The synchronous motor speed in (rpm) b.) Engine displacement. c.) rotor frequency at full load. d.) If the kilowatt hour costs $ 185.39. The money saved in energy consumption if the engine works continuously for three years and is replaced by an engine with 97%...
A motor apply power 10-hp split-phase motor speed at 1700 rpm is used to drive a...
A motor apply power 10-hp split-phase motor speed at 1700 rpm is used to drive a rotary pump, which operates 24 hours per day. An engineer has specified a 7-in small sheave, an 10-in large sheave, and three C112 belts. The service factor of 1.2 was augmented by 0.1 because of the continuous-duty requirement. Analyze the drive and estimate the belt life in passes and hours.
A centrifugal pump is driven at 1300 rpm by a 10 hp motor and delivers 250...
A centrifugal pump is driven at 1300 rpm by a 10 hp motor and delivers 250 GPM at 85 Fahrenheit water against 75 ft water head, assuming that the initial pump efficiency is 65 % doesn’t vary appreciably the maximum flow the pump can deliver is most nearly
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT