Question

In: Physics

The output of a generator is 440 V at 20 A. It is to be transmitted...

The output of a generator is 440 V at 20 A. It is to be transmitted on a line with resistance of

0.60 ?. To what voltage must the generator output be stepped up with a transformer if the
power loss in transmission is not to exceed 0.010% of the original power?
A) 7.3 kV B) 45 kV C) 22 kV D) 30 kW E) 4.4 kV

Solutions

Expert Solution

Even though the question mentions some original power, the power to be transmitted remains the same as 8800 W

Therefore,

Power transmitted = 440 x 20 = V x I.

Where V and I are the current and voltage after stepping up or stepping down the voltage.

(Note that there is no original or unoriginal power, both remain the same, the voltage and current differ)

From the above equation there are unlimited values for V and I.

If any one of the voltage or current is given, we can find the other.

In the problem a way is given to find the value of this current.

It is given that power loss must be so much. That is .01 % of the original power.

This is a loss of power in the transmission line and is affected by the value of the current that the generator sends through it.

If 20 A passes through 0.6 ohm the loss will be = 0.6 x 20 x20 = 240 W.


Now starts the confusion.

What should be the power loss expected after the transformer is used? Should the loss be 0.01% of this original power loss of 240 W or 0.01 % of the generator power? What is in the mind of the questioner cannot be understood. I mean the person who set the question originally and not you who posted the question.

However, we can solve the problem taking one first and then the other.

If the loss is 0.01 % of 8800 W, then it is 0.88 W

Hence the current is limited to ? [0.88 /0 .6] = 1.21 A

Using this value of current in the original power balance equation

440 x 20 = V x I.

V = 7266.36 volt.


If the loss is 0.01 % of 240 W, then it is 0.024 W

Hence the current is limited to ? [0.024 /0 .6] = 0.2 A

Using this value of current in the original power balance equation

440 x 20 = V x I.

V = 44000 volt. = 44 kV

ans.E) 44 kV


Related Solutions

The output voltage of an AC generator is given by ?v = 121 V sin (32?t)....
The output voltage of an AC generator is given by ?v = 121 V sin (32?t). The generator is connected across a 0.007 H inductor. Find the following. (a) frequency of the generator?=____ Hz (b) rms voltage across the inductor?=____ V (c) inductive reactance?=____ ohms (d) rms current in the inductor?=____ A (e) maximum current in the inductor?=____ A (f) average power delivered to the inductor?=____ W (g) Find an expression for the instantaneous current. (Use the following as necessary:...
An AC generator with an output rms voltage of 18 V at a frequency of 60...
An AC generator with an output rms voltage of 18 V at a frequency of 60 Hz is connected across a 3
The output voltage of an AC generator is given by V = (1.20×10^2) sin (30 pie...
The output voltage of an AC generator is given by V = (1.20×10^2) sin (30 pie t) (V). The generator is connected across a 0.500 H inductor. Find the (a) frequency of the generator, (b) rms voltage across to the inductor (c) inductive reactance, (d) rms current in the inductor, (e) maximum current Indian doctor, and (f) average power delivered to the inductor. (g) find an expression for instantaneous current. (h) At what time after t = 0, does the...
A 2000 v signle phase synchorunus generator isbeing used as a backup generator outside a diagnostic...
A 2000 v signle phase synchorunus generator isbeing used as a backup generator outside a diagnostic center in Islamabad . when the generator terminals are short circuited and a field exication current if 2.5 A is passed, the ammeter between the terminals read 100 A of full load current . if this terminals of the same generator are opened and the voltage across them is measured using a voltmeter , we get the value of 500V with the same exciatation...
A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic...
A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic center. When the generator terminals are short-circuited and a field excitation current of 2.5 A is passed, the ammeter between the terminals read 100 A of full load current. If the terminals of the same generator are opened and the voltage across them is measured using a voltmeter, we get the value of 500 V with the same excitation current. The armature resistance is...
A 3-phase, 20 kVA, 208 V, 4-pole Y-connected synchronous generator has a synchronous reactance of Xs...
A 3-phase, 20 kVA, 208 V, 4-pole Y-connected synchronous generator has a synchronous reactance of Xs = 1.5 W per phase. The resistance of the stator winding is negligible. The machine is connected to a 3-phase 208 V infinite bus. Neglect losses. The field current and the mechanical input power are adjusted so that the synchronous machine delivers 10 kW at 0.8 lagging power factor. Determine the excitation voltage Ef and the power angle d. The mechanical input power is...
A 1200 kW, 550 V DC generator has a terminal voltage of 500 V at rated...
A 1200 kW, 550 V DC generator has a terminal voltage of 500 V at rated current. It is being driven at a speed of 400 rpm. The armature resistance is 0.0009 Ω. a. Determine the armature voltage. b. Determine the developed torque. c. Determine the armature copper loss.
A generator with an rms voltage of 130 V is connected in series to a resistor...
A generator with an rms voltage of 130 V is connected in series to a resistor 3.65 kΩ and a capacitor 3.00 μF . 1. At what frequency must this circuit be operated for the current to lead the voltage by 29.0 ∘? (Answer Hz) 2. Using the frequency found in part A, find the average power consumed by this circuit. (Answer in W) ------------------------------------------ A 1.6-m wire is wound into a coil with a radius of 3.2 cm. 1....
An ac generator with a frequency of 30.0 Hz and an rms voltage of 14.0 V...
An ac generator with a frequency of 30.0 Hz and an rms voltage of 14.0 V is connected to a 65.0 μF capacitor. 1. What is the maximum current in this circuit? 2. What is the current in the circuit when the voltage across the capacitor is 4.30 V and increasing? 3. What is the current in the circuit when the voltage across the capacitor is 4.30 V and decreasing?
Write an expression for the instantaneous voltage ?(?) delivered by an ac generator supplying 120 V...
Write an expression for the instantaneous voltage ?(?) delivered by an ac generator supplying 120 V rms at 70 Hz. Assume the voltage is 0 at time ?=0, and leave the factors in exact form; do not round their values. Write the argument of the sinusoidal function to have units of radians, but omit the units.
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT