Question

In: Electrical Engineering

A 2000 v signle phase synchorunus generator isbeing used as a backup generator outside a diagnostic...

A 2000 v signle phase synchorunus generator isbeing used as a backup generator outside a diagnostic center in Islamabad . when the generator terminals are short circuited and a field exication current if 2.5 A is passed, the ammeter between the terminals read 100 A of full load current . if this terminals of the same generator are opened and the voltage across them is measured using a voltmeter , we get the value of 500V with the same exciatation cureent . the armature resistance is 0.8 ohms.

Determine the voltage regulation of this generator if it is delivering 100 A during normal operating with unity power factor , 100A with 0.8 leading PF and with 0.71 lagging PF

Solutions

Expert Solution


Related Solutions

A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic...
A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic center. When the generator terminals are short-circuited and a field excitation current of 2.5 A is passed, the ammeter between the terminals read 100 A of full load current. If the terminals of the same generator are opened and the voltage across them is measured using a voltmeter, we get the value of 500 V with the same excitation current. The armature resistance is...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a Y-connected load. The transmission line has an impedance of (0.02+j0.4) Ω/phase, and the load has an impedance of (4+j3) Ω per phase. Determine the;(a)line current (IL) at the load [2Marks] (b)line and phase voltage of the load[2 Marks](c)active power, reactive and apparent power [2 Marks](d) power factor and specify whether it is lagging or leading. [4 Marks]
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
Present the single-phase equivalent circuit of a synchronous generator.
Present the single-phase equivalent circuit of a synchronous generator.
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and...
Diesel Generator A I MVA diesel three-phase generator is rated at 4.16 kV, 60 Hz, and connected as Y its neutral is kept floating. It is directly tied to three loads, one consuming 50% of its capacity, and each of the other two consuming 25% of its capacity. A three-phase to ground fault could occur at any of the loads. Draw a one-line diagram of this system, then describe what type of faults could occur in the generator and diesel...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding...
A 3-phase, 5 kVA, 208 V, 4-pole, 60 Hz, star-connected synchronous generator has negligible stator winding resistance and a synchronous reactance of 8 Ω per phase at the rated terminal voltage. The generator is connected in parallel to a 3-phase, 208 V, 60 Hz infinite bus. All losses may be neglected. a)   Determine the excitation voltage and the power angle when the machine is delivering rated apparent power at 0.8 PF lagging. b)   If the field excitation is increased by...
A 1200 kW, 550 V DC generator has a terminal voltage of 500 V at rated...
A 1200 kW, 550 V DC generator has a terminal voltage of 500 V at rated current. It is being driven at a speed of 400 rpm. The armature resistance is 0.0009 Ω. a. Determine the armature voltage. b. Determine the developed torque. c. Determine the armature copper loss.
A generator with an rms voltage of 130 V is connected in series to a resistor...
A generator with an rms voltage of 130 V is connected in series to a resistor 3.65 kΩ and a capacitor 3.00 μF . 1. At what frequency must this circuit be operated for the current to lead the voltage by 29.0 ∘? (Answer Hz) 2. Using the frequency found in part A, find the average power consumed by this circuit. (Answer in W) ------------------------------------------ A 1.6-m wire is wound into a coil with a radius of 3.2 cm. 1....
Explain with the diagram the structure and theory of the work of a three-phase electric generator,...
Explain with the diagram the structure and theory of the work of a three-phase electric generator, specifying the function of each part ؟؟
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT