In: Mechanical Engineering
Statement:
Selection of compressor and refrigerant for HVAC system that is
operating on Vapor Compression Refrigeration System. The heat load
is 120,000 BTU/hr and temperature is to be maintained at space is
50C.
Step 1:
Select ambient and environmental conditions
Step 2:
Select refrigerant, preliminary calculations, use of property
charts, suction discharge pressure of compressor to achieve
required cooling, compressor capacity etc.
Step 3:
Select compressor (Stage, rpm, displacement, size etc)
need detailed solution
1 room temperature 50c
condenser coil temperature = 60c
outside temperature = -10c
ambient pressure 1bar
2 refrigerant - R134a
heat load = 120,000btu/hr or 35.16kJ
condenser pressure P2 = 16.18bar(discharge of compressor )
t2 = 70
specific energy lost bby condenser = h2-h3 = 438-288 = 150kJ/kg
mass flow rate of refrigerant m = 35.16/150 = 0.23kg/sec
no subcooling
evaporator temperature -10deg c assuming isentropic expansion
specific energy gained by the evaporator = h1-h4 = 394-288 = 106kJ/kg
specific workdone by compressor = 150-106 = 44kJ/kg
suction pressure of compressor = 2.006bar
3
single stage compressor
specific volume at stage1 v1 = 0.09959m^3/kg
volume flow at suction Qc = m*v1 = 0.023m^3/sec
p1 = 2.006 bar
p2= 16.18 bar
compression ratio = 16.18/2.006 = 8.065
stroke of cylinder = 0.2m
bore of cylinder = 0.1m
swept volume of cylinder V = .2*(.1^2*0.785)m^3 = 1.57*10^-3m^3
hence the size of compressor = 1.57Lt
speed of rotation = N rpm
volume flowrate = V*N/(2*60)m^3/sec
which is equal to v1 = 0.023 = 1.57*10^-3*N/(2*60)
hence the speed of compressor N = 1757.96RPM