Question

In: Civil Engineering

Arrive at the size of the rectangular RCC footing for a column of size 300 mm...

Arrive at the size of the rectangular RCC footing for a column of size 300 mm × 450 mm supporting an axial service load of 1200 kN. The SBC of soil is 200 kN/m2. Take M30 grade concrete, Fe415 steel, the angle of internal friction of soil is 300 and unit weight of soil is 19 kN/m3.

           

Solutions

Expert Solution

Answer) To arrive at the size of the rectangular footing we have

Area of the footing = (Dead load of structure, footing and surcharge + live load on column or wall)/ safe bearing capacity of the soil.

we are given axial Service load on column =1200KN

Dead load of structure, footing and surcharge is not given but they are generally considered as 10%of the load on column = 0.10*1200=120KN

Safe Bearing capacity of the soil is given = 200KN/m2

Now Area of footing is given by= (120+1200)/200

Area of footing =6.6m2

As no restricton is given on length and breadth of the footing we can Assume any size for footing (say) L=1.2B

1.2B2 =6.6

B2= 5.5

B=2.35m

and L= 1.2*2.35

L=2.82m

Approximate depth of foundation is given by Df=

Where qa = Safe Bearing capacity of the soil is given = 200KN/m2

= unit weight of the soil =19KN/m3

= Angle of internal friction of soil = 30

Df=

Df=1.17m

Use footing of 2.82m x 2.35m of footing at a depth of 1.17m.


Related Solutions

What will be the length (L in meter) of a rectangular footing to support rectangular column...
What will be the length (L in meter) of a rectangular footing to support rectangular column 20x70 cm and carries a dead load of 625 kN and live load of 426 kN. The net allowable bearing pressure is 155 kPa. The design should be according to (ACI) code with the following parameters: fc’ = 28 MPa, fy = 420 MPa.
Design for britishcode 8110 Design a square pad footing for a 300 mm square column supporting...
Design for britishcode 8110 Design a square pad footing for a 300 mm square column supporting a factored axial load of 800 kN. Safe bearing capacity of soil is 200 kN/m2, fcu=20 N/mm2, fy=415 N/mm2.Design a square pad footing for a 300 mm square column supporting a factored axial load of 800 kN. Safe bearing capacity of soil is 200 kN/m2, fcu=20 N/mm2, fy=415 N/mm2.
Design a square concrete column footing to support a 500-mm x 500-mm reinforced concrete column. The...
Design a square concrete column footing to support a 500-mm x 500-mm reinforced concrete column. The center of the column and footing must coincide. Loads: ???=350 ??, ???=480 ??, ???=100 ??−?, ???=130 ??−? Column Design Criteria: ??′=28 ???, ??=400??? Footing Design Criteria: ??′=28 ???, ??=400???, ??=175 ???,??=1.50 ?, ??=16 ??/?3,??=24 ??/?3, ??=20 ??, assume a thickness of the footing of 500 mm.
Design a square concrete column footing to support a 400-mm x 400-mm reinforced concrete column. The...
Design a square concrete column footing to support a 400-mm x 400-mm reinforced concrete column. The center of the column and footing must coincide. Loads: ???=350 ??, ???=480 ??, ???=100 ??−?, ???=130 ??−? Column Design Criteria: ??′=28 ???, ??=400??? Footing Design Criteria: ??′=28 ???, ??=400???, ??=180 ???,??=1.70 ?, ??=16 ??/?3,??=24 ??/?3, ??=25 ??, assume a thickness of the footing of 700 mm.
What will be the width (B in meter) of a square footing to support rectangular column...
What will be the width (B in meter) of a square footing to support rectangular column 40x40 cm and carries a dead load of 614 kN and live load of 477 kN. The net allowable bearing pressure is 180 kPa. The design should be according to (ACI) code with the following parameters: fc’ = 28 MPa, fy = 420 MPa.
Design a rectangular footing for an 18-in square interior column with a dead load of 210...
Design a rectangular footing for an 18-in square interior column with a dead load of 210 k and a live load of 180 k. Make the length of the long side equal to twice the width of the short side, fy = 60,000 psi, fc' = 4000 psi, normal weight, and qallowable= 3650 psf. Assume the base of the footing is 5 ft 0 in below-grade , γ concrete = 150 pcf and γ soil = 100 pcf. Also, assume...
Design an isolated rectangular footing to support an interior column 40 cm × 40 cm in...
Design an isolated rectangular footing to support an interior column 40 cm × 40 cm in cross section and carries a dead load of 800 kN and a live load of 600 kN. Use f́c= 21 MPa, fy= 420 MPa, q all (net) =200 kN / m2 , γsoil = 17 kN /m3 , and Df =1.25 m. Space limitations are such that one lateral dimension cannot exceed 2.5 m
A rectangular beam has a width of 300 mm and an effective depth of 510 mm....
A rectangular beam has a width of 300 mm and an effective depth of 510 mm. It carries Vu = 200 KN and Mu = 55 KN-m and is reinforced with 2650 mm2. Use f’c = 21 MPa and fy = 345 MPa. Normal concrete. Express your answer in two decimal places. a. Compute the shear strength in KN provided by concrete using the less conservative formula as shown. Express your answer in two decimal places. b. Calculate the required...
Investigate the adequacy of the square footing. The column has dimension of 500 mm x 500...
Investigate the adequacy of the square footing. The column has dimension of 500 mm x 500 mm and carries an axial load of 1210 KN dead load and 650 KN live load. Allowable soil pressure is 240 Kpa. There is 0.7 m height of soil having a unit weight of 15.74 KN/m3, fc’ = 20.7 Mpa, fy = 276.5 Mpa. The footing section is 2.8 m x 2.8 m with a 600 mm thickness. Use 25 mm diameter main bars.
A smooth rectangular duct 300 mm by 400 mm carries air at a rate of 1...
A smooth rectangular duct 300 mm by 400 mm carries air at a rate of 1 m3/s. Take the density of air to be 1.204 kg/m3 and the dynamic viscosity of air to be 1.825x10-5 kg/ms. Calculate the friction factor for the duct.