In: Electrical Engineering
The neutral point of 25MVA, 11kW alternator is
grounded through a resistance of 5Ω, the relay is set of operate
when there is an out of balance current of 2A. The CTs used have a
ratio of 1000/5. Calculate (neglect resistance of
alternator):
i. The percentage of stator winding protected against earth
fault.
ii. The minimum value of earthing resistance to protect 95% of the
winding.