Question

In: Electrical Engineering

1. In a power system with negligible resistance, the three-phase fault current at a point is...

1. In a power system with negligible resistance, the three-phase fault current at a point is 8 pu. The series reactance to be inserted at the fault point to limit the short circuit current to 5 pu

2. A 3-phase, 15 MVA, 10 kV alternator has internal reactance of 6% and negligible resistance. Find the external reactance per phase to be connected in series with the alternator so that steady current on short circuit does not exceed 6 times the full load current.

3. A 3-phase, 13.8 kV, 50 MVA alternator has positive, negative and zero sequence of 0.20, 0.20 and 0.05 pu. If the alternator is on no-load, determine the fault current for a three-phase fault.

Solutions

Expert Solution


Related Solutions

For a balanced three-phase system, show that the total power is constant. ?
For a balanced three-phase system, show that the total power is constant. ?
Describe Hydraulic steering gear system and power fault operation
Describe Hydraulic steering gear system and power fault operation
1. In a certain pint in an electrical system, the available fault current is 12 pu....
1. In a certain pint in an electrical system, the available fault current is 12 pu. Determine the actual fault current using a base power of 100 MVA and a base voltage of 34.5 kV 2. The positive, negative and zero sequence reactances of a 20 MVA, 13.2 kV synchronous generator are 0.3 pu, 0.2 pu and 0.1 pu respectively. The generator is solidly grounded and is not loaded. A line to ground fault occurs on phase a. Neglect all...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a Y-connected load. The transmission line has an impedance of (0.02+j0.4) Ω/phase, and the load has an impedance of (4+j3) Ω per phase. Determine the;(a)line current (IL) at the load [2Marks] (b)line and phase voltage of the load[2 Marks](c)active power, reactive and apparent power [2 Marks](d) power factor and specify whether it is lagging or leading. [4 Marks]
Generally, a single-phase power is commonly found in domestic households, whereas a three-phase power is preferable...
Generally, a single-phase power is commonly found in domestic households, whereas a three-phase power is preferable for larger demands. For safety purpose, over-current protection components are compulsory in the electrical distribution systems. i. Explain two advantages of a three-phase system compared to a single-phase system in the distribution system. ii. Briefly describe the characteristic and the function of two types over-current protection device installed in the distribution board (DB) residential building. iii. Miniature circuit breakers (MCB) with different current rating...
P = Power, V = Voltage, I = Current, and R = Resistance. Which of the...
P = Power, V = Voltage, I = Current, and R = Resistance. Which of the following relations is incorrect? Choices: V = I R P = V R P = VI I = V/R
Q1 (a) (i) Mention the types of short circuit fault in power system network. (ii) Briefly...
Q1 (a) (i) Mention the types of short circuit fault in power system network. (ii) Briefly explain the effects of short-circuit type of faults on a power system network.
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and...
2) A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant,...
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has...
A three-phase synchronous generator is rated 16 kV and 200 MVA, has negligible losses and has reactance of 1.65 pu. The generator is operated on an infinite bus of 15 kV voltage and delivers 100 MVA at 0.8 Power Factor, lagging. a)Determine the internal voltage (E_i), the power angle (δ), and the line current of the machine. b)If the field current of the machine is reduced by 10%, while the mechanical power input to the machine is maintained constant, determine...
A channel is the initial service point of a queuing system. A phase refers to the...
A channel is the initial service point of a queuing system. A phase refers to the number of stages that the service points provide. True or False?
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT