In: Civil Engineering
The air exchange coefficient for my home has been determined to
be 0.35 hr-1. My house volume is 13,757 ft3. Assume a constant
house temperature of 67 F.
For the West Face Wall, Area = 693 ft^2, total R-value (or U-value)
= 5.53 ft^2- F- hr / Btu.
Calculate:
[15] 1b the heat loss through the west wall for December 17
(average daily temperature was 1 °F). Note
that the HDD value needs to be multiplied by 24 (24 hrs / day) to
get the daily heat flux value
since R has units in hours.
[20]1c. The energy needed to heat air for Dec 17 (average daily
temperature was 1 °F).
Ans) We know,
Heat Loss (Q) = U A T
where, U = U-factor = 1/R value
A = Area of wall
T = Temperature difference
=> Q = (1 / 5.53) x 693 x (67 - 1)
=> Q = 8270.88 BTU/hr
Heat loss due to infilteration,Q' = 0.018 x ACH x V x T
where, V = volume
=> Q' = 0.018 x 0.35 x 13757 x (67 -1)
=> Q' = 5720.16 BTU/hr
Total heat loss = 8270.88 + 5720.16 = 13991 BTU/hr
=> Heat loss = 13991 BTU/hr x 24 hr/day = 335784 BTU
Ans) We know,
Energy required to heat air = specific heat capacity of air x weight x temperature difference
Specific heat capacity of air = 0.241 BTU/lb F
Density of air = 0.086 lb/ft^3
=> Weight of 13757 ft^3 air = density x volume = 0.086 lb/ft^3 x 13757 ft^3 = 1183.1 lbs
=> Energy required = 0.241 BTU/lb F x 1183.1 lb x (67 - 1) F
=> Energy required to heat air = 18818.38 BTU or 19854.44 kJ