In: Mechanical Engineering
Given:
Troom = 22 degree C = 295 K
Toutside = 2 degree C = 275 K
Vroom = Areaheight of ceiling = 25080.3048 = 609.6 m^3
Now,
Infiltration rate = 0.15 ACH = 0.15Vroom = 0.15609.6 = 91.44 m^3/hour
Now,
Mass of Supply Air entering = (pressurevolume of air entering) / (RTemperature)
= (10132591.44) / (287295)
= 109.43 kg/hour
= 109.43/3600 kg/s
Cooling load due to infiltrated air = mCp(Troom - Toutside)
= (109.43/3600)1.0216(22-2)
= 0.62107 kW
Hence, Total Energy consumption due to infiltrated air for 3 month period
= 0.62107 kW ( 3 months 30 days/month 24 hours/day )
= 1341.5 kWhr
If House is heated to 18 degree C instead of 22 degree C:
Troom = 18 degree C = 291 K
Mass of Supply Air entering = (pressurevolume of air entering) / (RTemperature)
= (10132591.44) / (287291)
= 110.93 kg/hour
= 110.93/3600 kg/s
Cooling load due to infiltrated air = mCp(Troom - Toutside)
= (110.93/3600)1.0216(18-2)
= 0.5037 kW
Hence, Total Energy consumption due to infiltrated air for 3 month period
= 0.5037 kW ( 3 months 30 days/month 24 hours/day )
= 1088 kWhr
Total Savings in electricity cost for 3 months = (1341.5 - 1088) kWhr 0.13 $/kWhr = 32.95 $
Please give positive rating if you liked the solution.