Given:
Troom = 22 degree C = 295 K
Toutside = 2 degree C = 275 K
Vroom = Areaheight
of ceiling = 250
8
0.3048
= 609.6 m^3
Now,
Infiltration rate = 0.15 ACH = 0.15Vroom
= 0.15
609.6
= 91.44 m^3/hour
Now,
Mass of Supply Air entering = (pressurevolume
of air entering) / (R
Temperature)
= (10132591.44)
/ (287
295)
= 109.43 kg/hour
= 109.43/3600 kg/s
Cooling load due to infiltrated air = mCp
(Troom
- Toutside)
= (109.43/3600)1.0216
(22-2)
= 0.62107 kW
Hence, Total Energy consumption due to infiltrated air for 3 month period
= 0.62107 kW
( 3 months
30 days/month
24 hours/day )
= 1341.5 kWhr
If House is heated to 18 degree C instead of 22 degree C:
Troom = 18 degree C = 291 K
Mass of Supply Air entering = (pressurevolume
of air entering) / (R
Temperature)
= (10132591.44)
/ (287
291)
= 110.93 kg/hour
= 110.93/3600 kg/s
Cooling load due to infiltrated air = mCp
(Troom
- Toutside)
= (110.93/3600)1.0216
(18-2)
= 0.5037 kW
Hence, Total Energy consumption due to infiltrated air for 3 month period
= 0.5037 kW
( 3 months
30 days/month
24 hours/day )
= 1088 kWhr
Total Savings in electricity cost for 3 months = (1341.5 - 1088)
kWhr
0.13 $/kWhr = 32.95 $