A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance...

A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance of 0.6 and negligible armature resistance. Its friction, windage and core losses are 1.2KW, 0.5KW and 1KW respectively .

  1. What is the speed of this motor?
  2. If this motor is initially supplying rated hp at 0.82 PF lagging . What are the magnitudes and angles of ?
  3. What is the power factor of the motor?
  4. How much induced torque and load torque is produced by this motor ?
  5. If is increased by 30 percent ,what is the new magnitude of the armature current?
  6. What is the motor’s new power factor?

Solutions

Expert Solution

Some words are missed so that solved both phase and line currents... Verify both


Related Solutions

A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24 ohms per phase. The armature resistance may be ignored. This motor is energized from 3.3-kV infinite bus bars. The field excitation is adjusted until unity power factor at rated load is achieved. Compute the maximum power and torque that the motor can deliver with the excitation remaining unchanged
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
396 v, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous...
396 v, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous reactance. Friction; wind; core losses and armature resistance are neglected. a) If the motor is operating under magnitude of phase current (ia) 216 Ampere and power factor of 0.6 lagging, 1. Find the input power of motor in hp ( 2. Find the generated voltage, EA 3. Find the torque and the maximum inducible torque in current state. b) If EA is increased by...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
A 450-V-rms, 50-Hz eight-pole delta-connected synchronous motor operates with a developed power (including losses) of 150...
A 450-V-rms, 50-Hz eight-pole delta-connected synchronous motor operates with a developed power (including losses) of 150 kW and a power factor of 0.9 lagging. The synchronous reactance is Xs = 1.6 ?. How much must the field current be increased to produce 100 percent power factor? Assume that Br is proportional to If with no magnetic saturation. (I would be very grateful if you could write neatly :) )
1. 414 Volt, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω...
1. 414 Volt, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous reactance. Friction; wind; core losses and armature resistance are neglected. a) If the motor is operating under magnitude of phase current (ia) 234 Ampere and power factor of 0.6 lagging, 1. Find the input power of motor in hp (10p) 2. Find the generated voltage, EA (10p) 3. Find the torque and the maximum inducible torque in current state. (10p) b) If EA...
A 400V, 2 pole, 50 Hz, three-phase induction motor is drawing 60 A at 0.85 PF...
A 400V, 2 pole, 50 Hz, three-phase induction motor is drawing 60 A at 0.85 PF lagging. The stator copper losses are 2 kW, the stator core losses are 1.8 kW and rotor copper losses are 700 W. The friction and windage losses are 600 W, the stray loss 100 W, and rotor core loss 100 W. Find the following quantities: a. The air gap power. b. The developed mechanical power. c. The output power. d. The efficiency of the...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and Its rated Line current is 100 A. if the generator is connected to a 480V grid Draw the phasor diagram and find EA, delta angle and output power under the following conditions a- The generator supply the rated current at 0.8 PF lagging. b-The generator supply the rated current at 1.0 PF. c- The generator supply the rated current at 0.8 PF leading.
500 hp, 600 V, 0.8 pf leading, 6-pole, delta-connected synchronous motor has XS = 1.2 ohm...
500 hp, 600 V, 0.8 pf leading, 6-pole, delta-connected synchronous motor has XS = 1.2 ohm and RA = 0 ohm. Assume motor is lossless. (a) Calculate EA and IA for 400 hp, 0.85 leading pf load. (b) What is the torque? (c) If |EA| is increased by 20% for the 400 hp load, what are the new values of IA and power factor?
A 3-phase, 380 V, 50 Hz , 6 pole, Y-connected induction motor has R1 = 0.1...
A 3-phase, 380 V, 50 Hz , 6 pole, Y-connected induction motor has R1 = 0.1 W , X1 = 0.4 W, R2’ = 0.12 W , X2’ = 0.4 W, Xm = 20 W , Pr = 1 kW. The motor is operated at 970 rpm what is the efficiency?
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT