Question

In: Electrical Engineering

A 450-V-rms, 50-Hz eight-pole delta-connected synchronous motor operates with a developed power (including losses) of 150...

A 450-V-rms, 50-Hz eight-pole delta-connected synchronous motor operates with a developed power (including losses) of 150 kW and a power factor of 0.9 lagging. The synchronous
reactance is Xs = 1.6 ?. How much must the field current be increased to produce 100 percent power
factor? Assume that Br is proportional to If with no magnetic saturation.

(I would be very grateful if you could write neatly :) )

Solutions

Expert Solution


Related Solutions

A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance...
A 400V, 50 Hz , 80 hp eight pole Δ connected synchronous motor has a reactance of 0.6 and negligible armature resistance. Its friction, windage and core losses are 1.2KW, 0.5KW and 1KW respectively . What is the speed of this motor? If this motor is initially supplying rated hp at 0.82 PF lagging . What are the magnitudes and angles of ? What is the power factor of the motor? How much induced torque and load torque is produced...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The following results were obtained from open circuit (no-load) and short circuit tests.             Open Circuit (no-load) Test Applied Stator Voltage VLine (V) Stator Line Current ILine (A) Total Input Power Pin (W) 240 9.6 536 220 7.2 420 200 5.4 352 180 4.3 304 160 3.5 276 140 3.0 248 120 2.5 224             Short Circuit (locked rotor) Test Applied Stator Voltage VLine (V) Stator Line...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0...
A 480 V, 50 Hz, Y-connected six-pole synchronous generator has a per-phase synchronous reactance of 1.0 Ω. Its full-load armature current is 60 A at 0.8 PF lagging. Its friction and windage losses are 1.5 kW and core losses are 1.0 kW at 60 Hz at full load. Assume that the armature resistance (and, therefore, the I2R losses) can be ignored. The field current has been adjusted such that the no-load terminal voltage is 480 V. a. What is the...
A 3 phase 460 V, 60 Hz, 4 pole, delta connected induction motor has the following...
A 3 phase 460 V, 60 Hz, 4 pole, delta connected induction motor has the following equivalent circuit parameters. Rs = 0.42 Ω, Rr = 0.23 Ω, Xs = Xr = 0.82 Ω. Xm = 22 Ω. The no load loss = 60 W and may be assumed constant. The rotor speed is 1750 rpm. Use the approximate equivalent circuit ( i.e. the Xm branch is at the very left of the circuit) determine the following a. the synchronous speed...
396 v, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous...
396 v, 60 Hz, 600 hp, 0.6 pf-leading, four-pole triangle connected synchronous motor has 0.9Ω synchronous reactance. Friction; wind; core losses and armature resistance are neglected. a) If the motor is operating under magnitude of phase current (ia) 216 Ampere and power factor of 0.6 lagging, 1. Find the input power of motor in hp ( 2. Find the generated voltage, EA 3. Find the torque and the maximum inducible torque in current state. b) If EA is increased by...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24...
A 1-MW, three-phase, star connected, 3.3-kV, 24-pole, 50-Hz synchronous motor has a synchronous reactance of 3.24 ohms per phase. The armature resistance may be ignored. This motor is energized from 3.3-kV infinite bus bars. The field excitation is adjusted until unity power factor at rated load is achieved. Compute the maximum power and torque that the motor can deliver with the excitation remaining unchanged
A 50-Hz, 440-V, 2 pole wye connected induction motor is rated at 75 kW. The equivalent...
A 50-Hz, 440-V, 2 pole wye connected induction motor is rated at 75 kW. The equivalent parameters are as follows: RS = 0.075 Ω RR’ = 0.065 Ω XS = XR’ = 0.17 Ω Xm = 7.2 Ω The losses associated with the machine are field and winding, miscellaneous and core loss with values of 1 kW, 150 W and 1.1 kW, respectively. For a slip of 4 %, determine a) The line current. (150.39  -23.08 A) b) The...
A 50-Hz, 440-V, 6 pole wye connected induction motor is rated at 75 kW. The equivalent...
A 50-Hz, 440-V, 6 pole wye connected induction motor is rated at 75 kW. The equivalent parameters are as follows: RS = 0.082 Ω; RR’ = 0.07 Ω; XS = 0.19 Ω; XR’ = 0.18 Ω; XM = 7.2 Ω The losses associated with the machine are field and winding, miscellaneous and core loss with values of 1.3 kW, 150 W and 1.4 kW, respectively. For a slip of 4 %, determine: a) The line current b) The stator power...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of...
A three phase, 60 Hz, 480 V, Y-connected, two-pole synchronous generator has a synchronous reactance of 0.95 Ω per phase. Its armature resistance is negligible. Its combined friction and windage losses are 1.3 kW and its core losses are 0.95 kW. The field current is constant at no-load. Its full load armature current is 55 A at 0.9PF lagging. Assume phase voltage is a reference. Determine following: a) Its terminal voltage when it is loaded with the rated current at...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and...
1- A 480-V, 60-Hz, delta connected, synchronous generator has a synchronous reactance of 0.5 ohm and Its rated Line current is 100 A. if the generator is connected to a 480V grid Draw the phasor diagram and find EA, delta angle and output power under the following conditions a- The generator supply the rated current at 0.8 PF lagging. b-The generator supply the rated current at 1.0 PF. c- The generator supply the rated current at 0.8 PF leading.