Question

In: Electrical Engineering

Problem 5: The following data refers to a 10-pole, 200 V, 50 Hz, 3 phase induction...

Problem 5: The following data refers to a 10-pole, 200 V, 50 Hz, 3 phase induction motor?

R1 = 3.5 ohm, X1 = 11 ohm, R`2 = 13.2 ohm. When the motor is tested on no-load, its observed that it takes 7.6 A (line current) and the total core loss is 620 W. B y using an approximate equivalent circuit at 8% slip, Calculate;

The rotor current
The supply current and power factor
Mechanical power developed.
Gross load torque
Determine the equivalent circuit

Solutions

Expert Solution

in the last page ...the heading is FOR STAR

and R01= R1 + R'2 = 13.2 + 3.5 = 16.7ohms...


Related Solutions

A 3-phase, 380 V, 50 Hz , 6 pole, Y-connected induction motor has R1 = 0.1...
A 3-phase, 380 V, 50 Hz , 6 pole, Y-connected induction motor has R1 = 0.1 W , X1 = 0.4 W, R2’ = 0.12 W , X2’ = 0.4 W, Xm = 20 W , Pr = 1 kW. The motor is operated at 970 rpm what is the efficiency?
A 440 V 4-pole 3 phase 50 Hz slip ring induction motor has its stator winding...
A 440 V 4-pole 3 phase 50 Hz slip ring induction motor has its stator winding mesh connected and its rotor winding star connected. The standstill voltage measured between slip rings with the rotor open –circuited is 218 V. the stator resistance per phase is 0.6Ω and the stator reactance per phase is 3Ω. The rotor resistance per phase is 0.05Ω and the rotor reactance per phase is 0.25Ω. Calculate the maximum torque and the slip at which it occurs....
A 3 phase 460 V, 60 Hz, 4 pole, delta connected induction motor has the following...
A 3 phase 460 V, 60 Hz, 4 pole, delta connected induction motor has the following equivalent circuit parameters. Rs = 0.42 Ω, Rr = 0.23 Ω, Xs = Xr = 0.82 Ω. Xm = 22 Ω. The no load loss = 60 W and may be assumed constant. The rotor speed is 1750 rpm. Use the approximate equivalent circuit ( i.e. the Xm branch is at the very left of the circuit) determine the following a. the synchronous speed...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction...
The following test data apply to a 110 kVA, 2300 V three-phase four-pole 60 Hz induction motor. No load test at rated voltage and frequency: Load current = 8.1 A, Three-phase power = 3025 W Blocked-rotor test at rated current and 15 Hz: Line voltage = 268 V, Three-phase power = 10.2 kW Stator resistance between line terminals = 2.34 Ω. Compute the stator current and power factor, kW output, and efficiency when this motor is operating at rated voltage...
A 400 V,50 Hz, six-pole three-phase induction motor drives a constant load of 140 N.m. The...
A 400 V,50 Hz, six-pole three-phase induction motor drives a constant load of 140 N.m. The motor has the following parameters ?1=0.294 Ω ?1=1.39 ?? ??=41 ?? ?2′=0.156 Ω ?2′=0.74 ?? 1) Starting. Calculate the following: i) Motor starting current. ii) Motor starting torque. 2) Maximum operating point. Calculate the following: i) Slip at which maximum torque is developed. ii) Maximum torque developed. 3) Steady-state operation. Calculate the following: i) Motor slip. ii) Motor speed. iii) Motor current. iv) Motor...
A 6-pole, 50 Hz, 3-phase induction motor running on full load develops a useful torque of...
A 6-pole, 50 Hz, 3-phase induction motor running on full load develops a useful torque of 160 Nm when the rotor emf makes 120 complete cycles per minute. The windage and friction loss is 1005.30 Watt. It is assumed; the core loss is lumped together with the windage and friction loss. The total stator loss is given to be 800 Watt. Compute: a) Shaft power output, b) The copper loss in the rotor winding,c) The input power to the motor, and d) The...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The...
Tests were carried out on a three-phase 220 V, 50 Hz, 4-pole delta-connected induction motor. The following results were obtained from open circuit (no-load) and short circuit tests.             Open Circuit (no-load) Test Applied Stator Voltage VLine (V) Stator Line Current ILine (A) Total Input Power Pin (W) 240 9.6 536 220 7.2 420 200 5.4 352 180 4.3 304 160 3.5 276 140 3.0 248 120 2.5 224             Short Circuit (locked rotor) Test Applied Stator Voltage VLine (V) Stator Line...
The parameters of a 3-phase, 4-pole, 50 Hz, Y-connected, wound-rotor induction motor are listed below. These...
The parameters of a 3-phase, 4-pole, 50 Hz, Y-connected, wound-rotor induction motor are listed below. These are the default values of the “Asynchronous Machine” model in MATLAB Simulink. r1=0.5968 ?; r2=0.6258 ?; L1=0.0003495 H; L2=0.005473 H; Lm=0.0354 H; Stator line voltage = 400 V rms. The motor for rotor speeds nm= 0 to 1500 rpm. X1= 0.1097 ohm, X2= 1.719 ohm , Xm= 11.12 ohm, RTH = 0.5853 , XTH = 0.1395 and VTH = 230.82 V. Suppose the motor...
A 400V, 2 pole, 50 Hz, three-phase induction motor is drawing 60 A at 0.85 PF...
A 400V, 2 pole, 50 Hz, three-phase induction motor is drawing 60 A at 0.85 PF lagging. The stator copper losses are 2 kW, the stator core losses are 1.8 kW and rotor copper losses are 700 W. The friction and windage losses are 600 W, the stray loss 100 W, and rotor core loss 100 W. Find the following quantities: a. The air gap power. b. The developed mechanical power. c. The output power. d. The efficiency of the...
A 50-Hz, 440-V, 2 pole wye connected induction motor is rated at 75 kW. The equivalent...
A 50-Hz, 440-V, 2 pole wye connected induction motor is rated at 75 kW. The equivalent parameters are as follows: RS = 0.075 Ω RR’ = 0.065 Ω XS = XR’ = 0.17 Ω Xm = 7.2 Ω The losses associated with the machine are field and winding, miscellaneous and core loss with values of 1 kW, 150 W and 1.1 kW, respectively. For a slip of 4 %, determine a) The line current. (150.39  -23.08 A) b) The...