1) A 25 kVA transformer supplies a load of 12 kW at power factor of 0.6...

1) A 25 kVA transformer supplies a load of 12 kW at power factor of 0.6 lagging. How much kVA can be added before the transformer is at rated load

a)when the added load is at 1.0 pf?

b)when the added load is at 0.866 pf leading?

Solutions

Expert Solution

SOLUTION:  

Givne 25kVA transformer supplies a load of 12kW at power factor 0.6lagging.


Related Solutions

2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is...
2.A n+400-k VA, 2300+n- 230+n-v, 60-hz transformer supplies a 0.8 lagging power-factor load whose KVA Is adjustable from no load to 120 percent rated KVA. The percent resistance, percent reactance, and percent core loss are m+1.56, m+3.16, and m+0.42 respectively. For 2 KVA increments of load, tabulate and plot the efficiency of the transformer from no load to 120 percent rated load. Use Matlab n=20 m=.2
A three-phase positive sequence Y-connected source supplies 12 kVA with a power factor of 0.75 lagging...
A three-phase positive sequence Y-connected source supplies 12 kVA with a power factor of 0.75 lagging to a parallel combination of a Y-connected load and a Δ-connected load. The Y-connected load uses 6 kVA at a power factor of 0.6 lagging and has an a-phase current of 12∠−30∘A Part A: Find the complex power per phase of the  Δ-connected load. (VA) Part B: Find the magnitude of the voltage. (Volts)
Q1. A station supplies 250 kVA at a lagging power factor (p.f) of 0·8. A synchronous...
Q1. A station supplies 250 kVA at a lagging power factor (p.f) of 0·8. A synchronous motor is connected in parallel with the load. If the combined load is 250 kW with a lagging p.f. of 0.9, determine : (i) the leading kVAR taken by the motor. (ii) kVA rating of the motor. (iii) p.f. at which the motor operates. Q2. A factory consists of the following (i) An induction motor of 150 h.p with 0.7 p.f lagging and 80%...
Table 1 Load Rating Power Factor Lighting 41.1kW 0.7 Lagging Lights 12.2 kVa 0.67 Lagging Ventilation...
Table 1 Load Rating Power Factor Lighting 41.1kW 0.7 Lagging Lights 12.2 kVa 0.67 Lagging Ventilation fans 9 kVa 0.7 lagging Heat pump 18 kW 0.707 Lagging misc equipment 11.3 kVa 0.55 lagging peak charging demand 209 kW unity Calculate the following for the car park using the data from Table 1: a) the maximum real power demand P (kW) b) maximum reactive power demand Q (kVAr) c) the total apparent power demand S (kVA) d) also, calculate the maximum...
How is it possible for a (Buck-Boost) Transformer to operate a KVA load many times larger...
How is it possible for a (Buck-Boost) Transformer to operate a KVA load many times larger than the transformers KVA rating?
Exercises 1. A 25 kVA single-phase transformer has the primary and secondary number of turns of...
Exercises 1. A 25 kVA single-phase transformer has the primary and secondary number of turns of 200 and 400, respectively. The transformer is connected to a 220 V, 50 Hz source. Calculate the (i) turns ratio, and (ii) mutual flux in the core. 2. A 25 kVA, 2200/220 V, 50 Hz single-phase transformer’s low voltage side is short-circuited and the test data recorded from the high voltage side are P=150 W, I1 = 5A and V1 = 40 V. Determine...
A transformer with rated power of 250 kVA and a secondary voltage of 230/400 V, 50...
A transformer with rated power of 250 kVA and a secondary voltage of 230/400 V, 50 Hz, delivers energy to the following loads: - 1 three-phase engine of nominal power 30 kW, 93% efficiency and power factor 0.9 - 90 lightning systems of 250 W each, rated voltage 230 V, and cos(phi)=0.6 (i), connected in a balanced manner Consider a direct sequence and a reference of voltages V1=V∠0º Find: a) The true, reactive and apparent power provided by the transformer...
Consider a space with a peak load of 18 kW with sensible heat factor, SHF, of...
Consider a space with a peak load of 18 kW with sensible heat factor, SHF, of the space is equal to 0.65. The space is maintained at 25 deg C and 50% RH. Find the appropriate condition (temperature and RH) of air entering the space. Also estimate the volumetric flow rate required in L/s. Show your calculations for at least two iterations with assumed inlet temperature of the air, Ta,i.
The performance for a power factor of 1 of a 200KVA, 3000/380 V single phase transformer...
The performance for a power factor of 1 of a 200KVA, 3000/380 V single phase transformer is 0.98 for both full load and medium load. The vacuum power factor is 0.2 and the voltage drop at full load with a power factor of 0.8 is 4%. Determine the parameters of the equivalent circuit of the transformer referred to the primary side.
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8...
The efficiency of a 400-kVA, single-phase, 60-Hz transformer is 98.77% when delivering full-load current at 0.8 power factor, and 99.13% with half-rated current at unity power factor. calculate: (a) The iron loss. (b) the full-load copper loss. (c) the efficiency at 3/4 load, 0.9 power factor
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT