1. Introduction
Traditionally, building high-voltage power lines has had few
obstacles during their construction
phase. Currently, this type of infrastructure is facing a number of
setbacks: it has a considerable impact
on the environment, on economic activities, and on the expansion of
cities, besides its economic cost,
including inspections and maintenance. All of these problems have
led the companies that use and
maintain this infrastructure to consider making the best use
possible of the existing lines before placing
new lines. Old lines were designed according to the standards of
the time in which they were built and
they were designed to bear a certain load. In many cases, these
towers were designed over forty years
ago, so the increased loads that will be placed on them will be far
greater than the one for which they
were designed. In addition to this fact, the design and execution
data of the towers has, in most cases,
disappeared, and in other cases, building regulations did not even
exist at the time. Due to this,
addressing the re-use of existing power lines requires a geometric
and structural analysis of the towers to
assess their current state.
Formerly, the towers’ dimensional analysis was performed through
expeditious and manual methods
(through the use of a gauge and a measuring tape) that required
direct contact with the structure and,
therefore, meant high risks and high costs. Afterwards, in search
of a remote non-invasive measuring
method, classic topographic measuring allowed thorough, notably
intense, field work taking angular
measurements and determining singular points indirectly through
angular intersections. More recently, the
existence of reflectorless electromagnetic surveying equipment has
allowed direct measurement of
distances and angles from a single point, making field work easier
and more efficient, although it solely
focuses on extracting unique and specific measurements determined
by the topographer [1]. This has meant
great uncertainty upon the elements of the tower, since the data
was only taken at the point where the
measurement is performed. In order to have the full representation
of the geometry of the structure, in the
last years laser scanning has presented as an interesting solution
[2,3,4,5], due to the fact that they
generate dense real-time point-clouds of the tower’s geometry from
a distance [6]. However, one of the
major limitations of these terrestrial geotechnologies is the
overall height of the tower, impossible to
cover completely from the ground, which has led to the use of
robotic unmanned aerial systems that
take aerial images and, through photogrammetric procedures, obtain
dense three-dimensional models
of this type of infrastructure [7].
As for structural assessment, this kind of structure has been
analyzed from different points of view
as presented in the literature: the effects of loading in the
stability of the tower [8–11]; the effects of
the stiffness of connections [12–14]; and causes of failure
[15–17]. No previous work was performed
in order to evaluate the effect of geometric imperfections such as
misalignments of structural members
at joints or assembly imperfections.Geometric Modeling
The geometric modeling of the transmission towers was performed
following four steps:
1. Cleaning and segmentation of point clouds in order to remove
undesired data, such as
reflections, noise or sensor artifacts. This step was performed
manually.
2. Alignment of the point clouds from each scan under a common
coordinate system. An
automated registration method, iterative closest point (ICP) [25],
was applied, supported by the
identification of matching points and minimizing the Euclidean
distance between
corresponding point clouds. Initial approximations (three points)
were manually identified by
the user, trying to guarantee a good distribution around the area
of interest and along the three
main directions (X, Y, Z). A solid-rigid transformation based on
the three points identified was
executed. Afterwards, an automatic iterative process to align the
different scans was performed
taking the Euclidean distance as a minimization criterion.
3. Generating cross-sections and technical drawings of the
electrical towers, focusing on the steel
profiles that make up each section of the tower and the arrangement
of the connections used to
define the linkage of these profiles. Different profiles were
automatically generated along each
main direction (X, Y, Z) in order to obtain vector information of
the main sections of the towers
and, thus, initial approximations to support the technical drawings
and CAD model generation.
4. Obtaining a computer aided design (CAD) model. Since the
structural analysis based on a FEM
model does not cope with dense laser models, an important step
which allows us to pass from
the 3D point clouds to a solid geometric model was performed. This
step consists in extruding the
sections obtained in the step before along its normal direction.
Manual interaction is required in
this step in order to solve the different intersections between
profiles and their connections. In
addition, specific existing libraries based on standard steel
profiles (i.e. L-shaped and U channel
profiles) were used for modeling the towers. Geometric modeling was
done using Geomagic
Spark, 2013 version.
3.3. Structural Analysis
The three towers are formed by angular steel profiles of different
dimensions, and given the age of
the towers and only for the purpose of the methodology developed in
this article, we assume the lower
specification for a steel material enabled by [26], type
S-235.
This brings the following mechanical properties: Young’s modulus of
2.1 × 108 kN/m2
, specific
weight of 76.9729 kN/m3
, Poisson’s coefficient of 0.3, and yield stress of 235 MPa.
Furthermore, the data of the power line, support type of the tower,
and the mechanical
characteristics of the electrical drivers are detailed below:
- High voltage power line with rated voltage of 132 kV and 50 Hz
AC
- Two duplex-circuit line with alignment support.
- Span: 300 m between supports.
Remote Sens. 2015, 7 11558
- Electrical driver of aluminum galvanized steel, type
LA-280.
The boundary conditions of the three towers are assumed to be
articulated supports in each of the
legs that make up the outer frame of the towers, so that they have
only limited movements according to
the global axes (X, Y, Z). The constraints upon the members are
explained in each of the structural
models discussed above.
The different load conditions are obtained according to [18]. The
following descriptions summarize
the loads, always bearing in mind that the towers are located in
the province of Guadalajara (Spain)
and that they are power lines with alignment support and with
suspension insulator strings [18].
- Permanent loads: The self-weight of the steel profiles that
comprise the towers, electrical
conductors, fittings, insulators, and the grounding wire.
- Wind load: It acts upon steel members of the towers, the
insulators, and the suspension
insulator strings.
- Imbalance of tensile forces: A longitudinal force equivalent to
25% of all unilateral tractions of
electrical drivers and grounding wire. This tensile force will be
applied at the point where the
electrical conductors and the grounding wire are attached to the
support, thus taking into
account the torsion that these forces could create.
- Electrical conductor failure: A unilateral tensile force related
to a single electrical conductor or
a grounding cable’s failure. The minimum admissible value for the
failure is 50% of the broken
cable’s tension in the power lines that have two conductors per
phase.
Taking into account aforementioned load patterns, the current
standards [18] refer to certain
calculation hypotheses that establish the load cases, shown in
Table 1.
Table 1. Load cases considered in structural analysis of
towers.
Tower Type Force Direction Hypothesis 1 Hypothesis 2 Hypothesis
3
Alignment support
and suspension
insulator strings
Vertical
Permanent loads, considering the electrical
conductors and the grounding cables to withstand
wind load according to a 120 km/h wind speed
Transversal
Wind load (120 km/h) on
electrical conductors, cables,
grounding cables and
supports of tower
Not applicable Not applicable
Longitudinal Not applicable
Imbalance of tensile
stress
Electrical
conductor and
grounding cable
failure
In order to clarify such load cases considered, in Figure 3 is
detailed upon finite element model of
one of the case studies herein analyzed (Tower 1), the arrangement
of the loads in each of the three
scenarios previously commented. Similarly, loads are arranged in
Towers 2 and 3
Experimental Results and Discussion
4.1. Case Studies
Since this study arises as a consequence of the need to analyze the
structural viability of a series of
electricity transmission towers that serve as support to an old
power electricity line located between the
cities of Guadalajara and Torija (Spain), three different cases
studies were chosen for the development
of the aforementioned methodology.
The electricity transmission towers chosen correspond to a type of
tower known as
“support alignment” which are disposed over different sections of
electricity line. Additionally,
in order to extend the study over different structural typologies,
each tower corresponds to a
different morphology.
The first tower is formed by both a main body support and another
principal body (comprising
horizontal bracings and diagonal bracings according to a St
Andrew’s disposition) and three horizontal
symmetrical bodies for the support of the cables. The second tower
only has a support body (formed
by horizontal bracings and secondary diagonal bracings according to
a St Andrew’s disposition) and
three asymmetric horizontal bodies. The third tower is similar to
the second one, with exception in the
diagonals forming the support body which are not arranged according
to a St Andrew’s disposition.
Figure 4 shows a photograph of the three towers that composes cases
studies described above.
Geometric Modeling
Following all steps described in Section 3.2, the point cloud data
obtained as a result of a laser
scanning survey was subsequently transformed into a CAD model valid
for its implementation in the
finite element software package SAP2000.
This is a key step required in this kind of reverse engineering
process, since data obtained from
laser scanning technology do not represent any valid information by
itself for the purpose of finite
element analysis without suitable data processing [27].
Therefore, taking this into account, CAD models for each one of
towers analyzed together with
drawings about its current disposition and assembly information
were obtained.
Figure 5 shows CAD wire models obtained for each one of towers
analyzed. Once such geometrical
models were obtained, they were directly imported as a DXF file to
SAP2000 software for the finite
element analysis stage.
Main geometric data concerns to dimensions of the base, height of
the tower, and length of
horizontal bodies are displayed in Table 2. The length of the
horizontal bodies of the towers is
measured from the main body of the tower up to the farthest node.
Tower 1 has three horizontal bodies
with different dimensions, while in towers 2 and 3, all the
horizontal bodies have similar dimensions.
Table 2. Main geometric data for transmission towers
analyzed.
Tower Base Dimensions (m) Height (m) Length of Horizontal Body
(m)
1 7.25 × 7.25 37.25
3.95
6.25
5.0
2 1.5 × 1.5 18.50 2.0
3 1.5 ×1.5 18.50 2.15