In: Mechanical Engineering
A counterflow, concentric tube heat exchanger used for engine cooling has been in service for an extended period of time. The heat transfer surface area of the exchanger is 5 m2, and the design value of the overall convection coefficient (without any fouling) is 38 W/m2K. During a test run, engine oil flowing at 0.1 kg/s is cooled from 110oC to 66oC by water supplied at a temperature of 25oC and a flow rate of 0.18 kg/s. Determine whether fouling has occurred during the service period. If so, calculate the fouling factor, R”f (m2K/W). Specific heat of engine oil is 2166 J/kgK, and water is 4178 J/kgK.
What is R”f = x 10-3 m2K/W?
during a test following data were collected
mh = 0.1 kg/sec
mc = 0.18 kg/sec
Cpoil = 2166 J/kgK
Cpwater = 4178 J/kgK
A = 5 m2
th1 = 1100C
th2 = 660C
tc1 = 250C
heat transfer from oil
Q = mcp(th2 - th1)
Q = 0.1 * 2166 * (110 - 66)
Q = 9530.4 J/sec
now,
heat rejected from oil = heat absorbed by water
moil cpoil (th2 - th1) = mwater cpwater (tc2 - tc1)
0.1 * 2166 * (110 - 66) = 0.18 * 4178 * ( tc2 - 25 )
tc2 = 37.6 0C
we know that, Logarithmic mean temperature difference (LMTD) is given by
where,
= th1 - tc2
= th2 - tc1
= 50.910C
Total heat transfer rate is given by
Q = Ud A
9530.4 = Ud * 5 * 50.91
Ud = 37.43 W/m2K
we can estimate fouling factor by the given relation
where
Ud = tested overall heat transfer coefficient (with fouling)
U0 = designed overall heat transfer coefficient (without any fouling)
put the values
Rf = 0.000397 m2K/W
Rf = 0.397 x 10-3 m2K/W