In: Other
liquid oil is used in the tube side of a shell-and-tube heat exchanger with two shell passes and four tube passes. water is heated in the shell side from 10°C to 50°C while the oil is cooled from 90°C to 60°C. the overall heat transfer coefficient is 53 W/m^2*K. the specific heat of the oil is 2.0 kJ/kg*K. Using the NTU - effectiveness method, calculate the area of the heat exchanger for a total energy transfer of 500 kW. what is the water flow rate for this heat transfer?
Here water is cold fluid which flows in shell side and oil is a hot fluid that flows in tube side.
Given: Initial and final temperature of water respectively, t1=100C=283.15 K and t2= 500C=323.15 K
Initial and final temperature of oil respectively, T1=900C=363.15 K and T2=600C= 333.15 K
Overall heat transfer coefficient, U=53 W/m2K
Specific heat of oil, Cpo= 2 kJ/kg K= 2000 J/kg K
Total energy transfer, q= 500 kW
For water, tc = t2-t1= 323.15 K-283.15 K= 40 K
For oil, Th= T1-T2= 363.15 K-333.15 K= 30 K
As the temperature difference for water is higher, it is the minimum fluid.
If the cold fluid is minimum fluid, effectiveness is calculated as
The energy transfer rate, q is given by
q=Co(Th)=Cw(tc)
where Cw is the Heat Capacity flow rate of water, which is the product of mass flow rate of water, w and specific heat of water, Cpw
Co is the Heat Capacity flow rate of oil, which is the product of mass flow rate of oil, o and specific heat of oil, Cpo
Consider q=Cw(tc)
Substitute the values of q and tc
Consider q=Co(Th)
Substitute for q and Th
Hence Cmin=Cw=12.5 kW/K and Cmax=Co=16.66 kW/K
Thus the capacity ratio, C is
Area of Heat Exchanger, A is obtained from the expression
where NTU is the Number of Transfer Units
From the Figure, Effectiveness of 2,4 Multipass Counterflow Exchanger Performance, the NTU corresponding to C=0.75 and =0.5 is 0.9.
Thus the area of heat exchanger is
Water Flow Rate, w is obtained using the expression
where Cw is the Heat Capacity flow rate of water
Cpw is the Specific Heat of water, Cpw=4.18 kJ/kg K
(W can be expressed as J/s)
Area of Heat Exchanger, A=212.26 m2 and Water Flow Rate, = 2.9904 kg/s