Question

In: Other

Consider the wall of Gypsum, Insulation, Concrete and Brick. It is located in a city for...

Consider the wall of Gypsum, Insulation, Concrete and Brick. It is located in a city for which the CDD is 800°C.days. The total area of the wall is 600 m2. The interior space is occupied and maintained at constant temperature 24 hours a day for a year. use the information below to answer these questions.

Tinside= 21°C

Toutside= 18°C

Gypsum: x=0.01 m, C=20 W/m2∙°C

Brick: x=0.12 m, k= 1 W/°C

Insulation: x=0.025 m, k= 0.04 W/°C

Block: x=0.20 m, C=5 W/m2∙°C

How much energy is required to cool the building over a year in GJ?

What is the cost to provide this energy if the cooling system is electrically and electricity costs $0.10/kWh with The COP for the cooling system is 2.4?

Solutions

Expert Solution

For heat flow by conduction, heat transferred per unit area is

Q (W) / A (m2)= [k (W/m C) *  T (C)] / L (m)= T(C) / R where R = L (m ) / k (W/m C) ...... eqn (1)

For heat flow by convection, heat transferred per unit area is

Q (W) / A (m2) = h (W/m2 C) *  T (C) = T (C) / R where R = 1 / h (W/m2 C) ...... eqn (2)

Solution

Gypsum: x=0.01 m, h=20 W/m2∙°C; hence from eqn (2) Rg = 1/ 20 = 0.05 m2∙°C/ W

Brick: x=0.12 m, k= 1 W/m°C ; hence from eqn (1) Rbr = 0.12 / 1 = 0.12 m2∙°C/ W

Insulation: x=0.025 m, k= 0.04 W/°C; hence from eqn (1) Ri = 0.025 / 0.04 = 0.625 m2∙°C/ W

Block: x=0.20 m, C=5 W/m2∙°C; hence from eqn (2) Rbl = 1/ 5 = 0.2 m2∙°C/ W

Total resistance = Rt = Rg + Rbr + Ri + Rbl = 0.05 + 0.12 +0.625 + 0.2 = 0.995 m2∙°C/ W

Hence from eqn (1) Qt = A * Tt / Rt in respective units .... eqn (3)

From data Tt (C) = (21-18) = 3 C and  A = 600 m2 ; From calculation Rt = 0.995 m2∙°C/ W

Hence after substituting in eqn (3) we get Qt = 1809 W = 1809 J/s. This is the heat loss through the system.

This heat loss need to be compensated from outside if the temperature in the building needs to be maintained at 21 C.

Time of maintaining the building under cooling over a period of 365 days= t= 365 day/year* 24 hr/day* 60 min/hr* 60 s/hr = 31536000 s

a) With 365 days in a year, energy required to cool the building =Q365= Qt* t = 1809 J/ s * 31536000 s = 57.05 * e9 J = 57.05 GJ

b) COP for heating system = Actual heat supplied per hour / Heat to be removed per hour

2.4 = QA / (Qt * 60 * 60) in consistent units

Hence QA (W) = 2.4 * (Qt * 60 * 60) = 2.4 * 1809 * 60 * 60 = 15629760 W

QA (W) = 15629760 W-h = 15629.8 kWh

Unit Cost is $0.10/kWh . Hence energy cost for one hour = $0.10/kWh * 15629.8 kWh = $1563 per hour

For 365 days or one year the total energy cost =   $1563 per hour * 24 h/day * 365 day/ year = $13.7 million


Related Solutions

Calculate the volume of mortar ( cf) for the following brick wall. A double wythe wall...
Calculate the volume of mortar ( cf) for the following brick wall. A double wythe wall 8-feet high by 14-feet wide having one opening 48-inches by 72-inches and one opening 32 inches by 48 inches. Mortar joints are 0.5-inches and there is 25% mortar waste. The joint thickness between the wythes is 0.5-inch thick and is grouted with mortar. There are 982 total bricks (3.75" x2.25" x8") for both wythes including 3% brick waste.
Design a wall footing to support a 30cm − wide reinforced concrete wall with a dead...
Design a wall footing to support a 30cm − wide reinforced concrete wall with a dead load DL =293 KN/m and a live load LL = 218 KN/m. The bottom of the footing is to be 1. 2m below the final grade, the soil weighs 16 KN m3 ⁄ , the allowable soil pressure, qa = 192 KN m2 ⁄ , and there is no appreciable sulfur content in the soil. fy = 420MPa and fc′ = 21MPa, normal- weight...
A wall footing is to support a 400 mm wide reinforced concrete wall with a dead...
A wall footing is to support a 400 mm wide reinforced concrete wall with a dead load of 270 KN/m and a live load of 210 KN/m. The bottom of the footing is 1.50 m below the final grade. Assume the soil weighs 15.78 KN/m3 and the allowable soil pressure is 190 Kpa. Use 75 mm as concrete cover, fc’ is 28 Mpa, fy is 415 Mpa, and concrete weights 23.5 KN/m3. Compute the: Width and depth of footing Spacing...
The composite wall of a building consists of a 100 mm layer of common brick, a...
The composite wall of a building consists of a 100 mm layer of common brick, a 100 mm layer of glass fibre (organic bonded), a 10 mm layer of gypsum plaster (perlite aggregate) and a 6 mm of pine panel. If the inside convection coefficient is 10 W/m2 .K and the outside convection coefficient is 70 W/m2 .K, calculate: (i) the total thermal resistance of the wall; (ii) the overall heat transfer coefficient of the wall.
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in...
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in a locality wherein water has excess of chlorides in it. Required average compressive strength of concrete has been determined to be 4700 psi. Beams have cross-section of 9 in. x 21 in. reinforced with 4 # 6 bars. Reinforcement has a concrete cover of 1.25 in. and there is a clear space of 1.0 in. between form surface and steel bars. Fine aggregate has...
Design a plain concrete footing for a 400 mm reinforced concrete wall that supports a DL...
Design a plain concrete footing for a 400 mm reinforced concrete wall that supports a DL = 185 KN/m and 95 KN/m live load. The base of the footing is to be 1.2 m below the final grade. fc’ = 20.7 Mpa and allowable soil pressure is 200 Kpa, weight of soil is 15.82 KN/m3. (ACI)
a) Explain differential movement and prevention in brick and concrete masonry. Where the control joints are...
a) Explain differential movement and prevention in brick and concrete masonry. Where the control joints are must be located. b) A 150 –ft exterior clay brick wall is designed for ½ -in expansion joints and a joint compressibility of 40 %. Determine the maximum joint spacing and the minimum number of joints required for entire wall. (Wall is going to be built in Lubbock TX. Temperature difference can be taken as 80ºF. Annual mean relative humidity is moderate 75>AMRH>50)
1. How is a brick veneer wall built? What are the correct steps in this process?...
1. How is a brick veneer wall built? What are the correct steps in this process? 2. Why do we need to use an SW brick for an exterior wall in New England? And what type of mortar should we use?
A 10-inch-thick concrete bearing wall of height 10’ is laterally supported at 20’. The wall is...
A 10-inch-thick concrete bearing wall of height 10’ is laterally supported at 20’. The wall is subjected to axial loads comprising of dead load of 20 kip/ft (including self-weight) and a live load of 15 kip/ft. The top and bottom of wall is restrained against lateral movement and there are no out of plane loads. Can the wall sustain applied loads? If so, determine the reinforcement required in wall. Use f’c = 4000 psi and fy = 60ksi show all...
Please choose the correct answer for problem 1,2,3,4 1) A brick wall has a thickness of...
Please choose the correct answer for problem 1,2,3,4 1) A brick wall has a thickness of 0.3 m, an area of 30 m2 , and a thermal conductivity of 0.7W/(m· ◦C). One side of the wall is at a temperature of 5◦C and the other side of the wall is at 25◦C. What is the energy/sec flowing through the wall due to conduction? A. 1000 W   B. 1200 W   C. 1400 W   D. 1600 W 2) A brick wall has...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT