Question

In: Physics

Three single-phase transformers are used in a Y-Y configuration to supply a load rated 4000 V,...

Three single-phase transformers are used in a Y-Y configuration to supply a load rated 4000 V, and drawing 80 kW at a power factor of 0.72 (lagging), independently of the voltage. Each transformer, rated 14500/2300 V, 40 kVA, has the following parameters in pu: series elements: 0.01 (resistive), 0.06 (inductive); magnetizing branch: 70 (resistive), 20 (inductive).

(a) Assume the transformer is ideal and the phase voltage at the primary is 13000 V. Draw the per phase equivalent circuit of the transformer and load. Give the phase voltage and current. Indicate if the transformer is overloaded. Compute the real and reactive power drawn from the feeder. Draw the per-phase V-I diagram and power diagram seen from the primary side.

(b) Draw the per phase equivalent circuit of the transformer, indicating parameters in pu and Ohm referred to the primary. Draw the equivalent circuit used under no-load and full load conditions seen from the primary side in pu and Ohm. For operation under load, draw the series impedance diagram and compute the impedance in Ohm and angle. Estimate the per phase transformer losses at rated voltage and current in pu and in kW. Find the efficiency for the given load. Indicate the impact on losses and efficiency of using a transformer with a 0.02 pu series reactance and a 100 pu core resistance.

(c) For rated voltage on the primary side and a short circuit across the load with an impedance of 0.10 pu resistive, compute the current in A as seen from the primary side. Draw the V-I diagram. Compute the current if the fault impedance is 0 and compare the 2 values. Indicate, for a 0.10 resistive short, the impact on the fault current of using a transformer with a 0.02 pu series reactance and a 100 pu core resistance. Compare the fault impedance and V-I diagrams.

Solutions

Expert Solution


Related Solutions

What is difference between a 120V/240V step-up and 240/120 V step-down single phase transformers? Both transformers...
What is difference between a 120V/240V step-up and 240/120 V step-down single phase transformers? Both transformers are rated 5 kVA and operated at 60 Hz. Explain your answer by means of relevant diagrams and equations.What is difference between a 120V/240V step-up and 240/120 V step-down single phase transformers? Both transformers are rated 5 kVA and operated at 60 Hz. Explain your answer by means of relevant diagrams and equations.What is difference between a 120V/240V step-up and 240/120 V step-down single...
b) The load connected to a three-phase supply comprises three similar coils connected in star. If...
b) The load connected to a three-phase supply comprises three similar coils connected in star. If the phase currents are 10A and the total active power and power factor absorb by the loads are 3kW and 0.8 lagging, respectively. Find: i. The magnitude of phase and line voltages ii. Total apparent power (1 mark) iii. The impedance of each coil. c) If the coil in Q3(b) are now connected in delta to the same three-phase supply, calculate the magnitude of...
Simulate a single phase to three phase converter. Show a) the circuit b) values used for...
Simulate a single phase to three phase converter. Show a) the circuit b) values used for each component c) input and output waveform d) explain how the circuit works
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of...
Three balanced 3-phase loads are connected in parallel. Load 1 is Y-connected with an impedance of 400 + j300 ? per phase, load 2 is ?-connected with an impedance of 2400 – j1800 ? per phase, and load 3 is absorbing 172.8 + j2203.2 kVA. The loads are fed from a set of distribution lines with an impedance of 2 + j16 ? per line. The magnitude of the line-to-neutral voltage at the load end of the line is 24?3...
Question 5 a) Draw the circuit of a Three-phase bridge inverter using a Y-connected load and...
Question 5 a) Draw the circuit of a Three-phase bridge inverter using a Y-connected load and explain its operation using 180 degree conduction clearly showing the gating sequence and the corresponding output line voltages for each phase. (10) b) For the Y-connected load determine the line to neutral voltages for the three modes of operations. Draw the equivalent circuits for each mode and then draw the phase voltage waveforms for the 180-degree conduction. (7)
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to...
A 280-V, 3Ø AC power system, Y-connected three-phase generator connected through a three-phase transmission line to a Y-connected load. The transmission line has an impedance of (0.02+j0.4) Ω/phase, and the load has an impedance of (4+j3) Ω per phase. Determine the;(a)line current (IL) at the load [2Marks] (b)line and phase voltage of the load[2 Marks](c)active power, reactive and apparent power [2 Marks](d) power factor and specify whether it is lagging or leading. [4 Marks]
A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic...
A 2000 V single-phase synchronous generator is being used as a backup generator outside a diagnostic center. When the generator terminals are short-circuited and a field excitation current of 2.5 A is passed, the ammeter between the terminals read 100 A of full load current. If the terminals of the same generator are opened and the voltage across them is measured using a voltmeter, we get the value of 500 V with the same excitation current. The armature resistance is...
A 400 V,50 Hz, six-pole three-phase induction motor drives a constant load of 140 N.m. The...
A 400 V,50 Hz, six-pole three-phase induction motor drives a constant load of 140 N.m. The motor has the following parameters ?1=0.294 Ω ?1=1.39 ?? ??=41 ?? ?2′=0.156 Ω ?2′=0.74 ?? 1) Starting. Calculate the following: i) Motor starting current. ii) Motor starting torque. 2) Maximum operating point. Calculate the following: i) Slip at which maximum torque is developed. ii) Maximum torque developed. 3) Steady-state operation. Calculate the following: i) Motor slip. ii) Motor speed. iii) Motor current. iv) Motor...
A three-phase balanced star load No. 1 of (120 +j90) ohms in parallel with another three-phase...
A three-phase balanced star load No. 1 of (120 +j90) ohms in parallel with another three-phase balanced star load No. 2 of (90 +j120) ohms, both are fed by three-phase balanced conductors of 3 ohms resistance and 4 ohms reactance. If the generator is 240 volts, with angle of -150° on phase c and reactance of 1 ohms, determine: a) the current on load N°1 on phase C, b) the terminal voltage of the generator on phase B, c) the...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed...
A three phase 10kW, 1700rpm, 60Hz, four poles, Y connected induction motor has a no-load speed of 1750rpm. The rotational mechanical losses are constant and equal to 500W. The core losses are constant and equal to 300W. The copper losses in the stator equal to the copper losses in the rotor at full load. If the rotor resistance per phase is 0.25?, calculate the following: a.The frequency of the induced current in the rotor circuit at full load. b.The percentage...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT