Question
Heat flow q = (mass flow rate) x (enthalpy change)
Prove the following with explanations.
q(Btu/hr) = 4.5(cfm)(Δh Btu/lb dry air)
q(Btu/hr) = 1.08(cfm)(ΔT) (dry bulb temperature in deg.F)
q(Btu/hr) = 4840(cfm)(Δw lb water/lb dry air)
where (cfm) is the air flow rate in cubic feet per minute.
Also, Show following for liquid water
q(Btu/hr) = 500(gpm)(ΔT deg.F)
where (gpm) is water flow rate in US gallons per minute
a) | To prove |
![]() |
|
We know from heat added formula | |
Q = m x Cp x dT | |
where | |
Q is heat added or subtracted to a substance | |
m - mass of the substance | |
Cp - specific heat of the substance | |
dT - change in temperature | |
But for room which is receiving heat from outdoor , where air is | |
moving in the room | |
Here we are dealing with air | |
![]() |
|
Specific heat of dry air at 80 F = 0.24 Btu /lb F ….. (1) | |
Specific heat of steam at 80 F = 0.445 Btu /lb F….. (2) | |
We know that at normal condition air contains some moisture . | |
Hence | |
Q = ma Cp a (dT) + mv Cp v (dT) | |
dividing RH and LH with some unit of time , to consider flow rate | |
![]() ![]() ![]() |
|
Putting values (1) &(2) | |
![]() ![]() ![]() |
|
For a typical air conditioning process, | |
the ratio mv/ma =0.01 | |
Hence ![]() ![]() |
|
![]() ![]() ![]() |
|
combining terms | |
![]() ![]() |
|
0.00445 is negligible value , Hence we can remove it from qequation | |
![]() ![]() |
|
What we intrested in volumetric flow (CFM) not in mass flow rate | |
we know, | |
mass = volume x density | |
mass flow rate = volume flow rate x density of air | |
![]() |
|
(density of air at standard condition = 1 /13.3 lb/ft^3) | |
Therefore ma dot lb/hour = 4.5 CFM | |
Putting this value in eq (3) | |
![]() |
|
when we simplify equaltion (4) in terms of enthalphy , | |
change in heat content of system, | |
![]() |
|
as specific heat of air into temperature change gives to change in enthalphy change of air | |
Thus | |
![]() |
|
b) | To prove |
Qs =1.08 (CFM ) dT | |
From equation (4) | |
![]() |
|
![]() |
|
crossing F | |
![]() |
|
multipling | |
![]() |
|
c) | To prove |
Ql = 4840 CFM dW lb water /lb dry air | |
For a room where air with vapor mass mv1 is entering & air with vapor mass mv2 is leaving | |
mass voume of vapour condesed in room mw | |
mw =mv2- mv1 | |
flow rates | |
![]() ![]() ![]() |
|
as per defination, ratio w = mass of vapor / mass of dry air | |
w = mv/mda | |
w = ![]() ![]() |
|
Rearranfing eq (5) | |
![]() ![]() ![]() ![]() ![]() ![]() ![]() |
|
but ![]() ![]() |
|
![]() ![]() |
|
![]() ![]() |
|
multiplying both sides of equation by latent heat of vaporization | |
hv x ![]() ![]() |
|
but hv x ![]() |
|
Thus Q latent = hv x ![]() ![]() |
|
Now for LH side | |
hv in Btu/lbm & ![]() |
|
crossing lbm , we will get LH side = Btu / hr | |
And for ![]() |
|
mass = volume x density | |
mass flow rate = volume flow rate x density of air | |
![]() |
|
(density of air at standard condition = 1 /13.3 lb/ft3) | |
Therefore ![]() |
|
putting this expression in equation (6) | |
Q latent = 4.5 CFM x (w2-w1) x hv -----(7) | |
from enthalphy table, | |
the enthalphy change from satured liquid to satured liquid at degree at | |
actual condesation process happening at | |
( process happens at 32 0F i.e 00C) | |
then enthalphy change at 32 F = 1075.2 btu/lbm | |
putting this value in equation (7) | |
Qlatent = 4.5 (CFM) x dW x 1075.2 | |
Q latent = 4838.4 (CFM) x dW | |
Rounding off | |
Q latent = 4840 x (CFM) x dW ------(c) |