Question

In: Mechanical Engineering

List the operating procedure to put the differential pressure transmitter into service and put it out...

List the operating procedure to put the differential pressure transmitter into service and put it out of service with suitable diagram.   

Solutions

Expert Solution

Answer:

Valve manifold is a very important accesory for any diffrential pressure transmitter. Most of the diffrential pressure transmitter either comes with 3 valve manifold or comes with 5 valve manifold and it is also available with single block and bleed valve manifold . We will discuss the diffrential pressure transmitter putting in service and putting out of service one by one.

3 valve manifold differential pressure transmitter:

Isolation and equilization of pressure from the process to the transmitter for the maintenance and calibration pupose is done by the manual valves. High and low pressure block valves are also available in this system.

DPT shown in figure is diffrential pressure transmitter

Procedure of putting 3 valve manifold diffrential pressure transmitter in to service:

  • Equalizing valve should be closed and all high pressure and low pressure valve to be chacked
  • After that equalizing valve should be opened. By this same pressure is applied at the both sides of the transmitter and it creates zero diffrential pressure
  • After this high pressure block to be opened very slowly and checking to be done for leakage from both high and low pressure side of the transmitter
  • After this equalizing valve is closed. This is used to lock the pressure at both sides of transmitter
  • After this low process block valve is made open so that the process pressure is applied at low pressure side of the transmitter and it leads to create the working diffrential pressure.
  • After doing all thiese steps, transmitter will come under serice or operation.

Removing the 3 valve manifold diffrential pressure transmitter from the service:

  • Very first, low pressure block valve need to be closed.
  • After this equalizing valve is made open
  • High pressure block valve is closed.
  • Transmitter is out of sevice after this but still pressure will be inside that should be bleeded

5 valve manifold differential pressure transmitter:

Procedure of putting 5 valve manifold diffrential pressure transmitter in to service:

  • Bleeding valve and Equalizing valve should be closed and all high pressure and low pressure valve to be chacked
  • After that equalizing valve should be opened. By this same pressure is applied at the both sides of the transmitter and it creates zero diffrential pressure.
  • After this high pressure block to be opened very slowly and checking to be done for leakage from both high and low pressure sides of the transmitter
  • After this equalizing valve is closed. This is used to lock the pressure at both sides of transmitter
  • After this low process block valve is made open so that the process pressure is applied at low pressure side of the transmitter and it leads to create the working diffrential pressure.
  • After doing all thiese steps, transmitter will come under serice or operation.

Removing the 5 valve manifold diffrential pressure transmitter from the service:

  • Very first, low pressure block valve need to be closed.
  • After this equalizing valve is made open
  • Opening of the beeding valve for venting process pressure in to the atmosphere
  • Transmitter is out of sevice after this but still pressure will be inside that should be bleeded

Sinlgle block and bleed valve manifold:

This is used for guage pressure applications. In this process, the low pressure port of the tranmitter is always vented to the atmosphere. Impulse lines are used to connect the high pressure port to the process medium For putting it in service one should ensure that initially both bleed and block valves are in closed condition and than block valve is slowly opened for taking the unit in to service

Removing single block and bleed valve manifold diffrential pressure transmitter from the service:

It is very easy to remove it from servive and it is done by just closing the block valve and opening of the bleed valve for venting the process pressure to the atmosphere.


Related Solutions

9) Look up the Rosemount 3051 Pressure Transmitter. a) What is the difference between the Differential...
9) Look up the Rosemount 3051 Pressure Transmitter. a) What is the difference between the Differential Pressure and Absolute Pressure measurement? b) What is the difference between Gage and Absolute pressure? c) What is the difference between the Coplanar Pressure Transmitter and the In-Line Pressure Transmitter? d) What is meant by HART Communication protocol. e) Is this transmitter approved for use with drinking water? Aboard ships? In China as intrinsically safe. f) Name all the transmitter output options.
Explain in detail using diagrams and schematic, the process of calibrating PX-70 Differential Pressure Transmitter (DPT)...
Explain in detail using diagrams and schematic, the process of calibrating PX-70 Differential Pressure Transmitter (DPT) to measure pressure in the range 0 to 4 psi.
Define the different component used to calibrate pressure transmitter
Define the different component used to calibrate pressure transmitter
convert differential equation to a matrix differential equation? can put an example and solve it.
convert differential equation to a matrix differential equation? can put an example and solve it.
1. (10 pts) A mobile receiver communicates with the transmitter at an operating frequency of 550...
1. (10 pts) A mobile receiver communicates with the transmitter at an operating frequency of 550 MHz at a distance of 3 km. Calculate the path loss in the system. 2. (15 pts) Assume that two antennas are half-wave dipoles and each has a gain of 3 dB. If the transmitted power is 1 W and the two antennas are separated by a distance of 10 km, what is the received power? Assume that the frequency is 100 MHz. 3....
List and describe the steps in the power-on procedure
List and describe the steps in the power-on procedure
procedure Example is X: Integer; procedure First is begin Put(X); -- Print X New_Line; -- Print...
procedure Example is X: Integer; procedure First is begin Put(X); -- Print X New_Line; -- Print a newline character end First; procedure Second is X: integer; procedure Third is X: Integer; begin -- Third x := 99; First; end Third; begin -- Second x := 88; Third; end Second; begin -- Example x := 77; First; Second; end Example; a) What will be printed by this program if we assume static scope? b) What will be printed by this program...
7) List the steps of the Gram stain procedure
7) List the steps of the Gram stain procedure
Procedure A: A piece of fresh liver and little bit of water was put inside of...
Procedure A: A piece of fresh liver and little bit of water was put inside of test tube. The test tube was put inside of boiling water for five minutes. Test tube was taken out from boiling water and drained out the water. 2 mL of hydrogen peroxide was put inside of the test tube and only little bubbles (enzyme activity ) were formed. Q1. What was the purpose of the assay performed? Q2. Did increasing the temperature (heating the...
A steam powerplant operating on an ideal Rankine Cycle is operating at a boiler pressure of...
A steam powerplant operating on an ideal Rankine Cycle is operating at a boiler pressure of 5.75MPa, steam enters the turbine at 500°C and expands to 147kPa. If the powerplant is producing 5MW of energy find the following: Enthalpies at each point of the cycle 1,2,3,B (hint: you will have to interpolate horizontally for point 1 and interpolate for the f,g,fg values for point 2) Net work in kj/kg Mass flow rate of throttle steam used by the powerplant Heat...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT