Pressure transmitter Calibration
Introduction
pressure is an important physical quantity.In industries it should be maintained ,controlled,monitored at specific readings so that’s why pressure transmitters are so important in industries . so calibration of pressure transmitter is what we are going to discuss now.
Equipments required for calibration of pressure transmitter
Pressure transmitter, multimeter, HART communicator
Basic procedure for calibration
If transmitter is analog transmitter
Apply 0% pressure as per LRV with hand held test pump and check multimeter if it is not 4ma adjust the zero pot in the transmitter and correct transmitter output to 4ma
In case of SMART Transmitter
small example of five point calibration is given below
Low range value=0psi
upper range value=200psi
PERCENT OF RANGE | INPUT PRESSURE | OUTPUT CURRENT(IDEAL) |
0% | 0 PSI | 4.00 mA |
25% | 50 PSI | 8.00 mA |
50% | 100 PSI | 12.00 mA |
75% | 150 PSI | 16.00 mA |
100% | 200 PSI | 20.00 mA |
75% | 150 PSI | 16.00 mA |
50% | 100 PSI | 12.00 mA |
25% | 50 PSI | 8.00 mA |
0% | 0 PSI | 4.00 mA |