Question

In: Civil Engineering

Design a mix for a 3,000 psi concrete to be used in an indoor basement slab....

Design a mix for a 3,000 psi concrete to be used in an indoor basement slab. Your gravel is an ASTM C33C #57 stone. Your fine aggregate grades as follows: No. 4 – 3%, No. 8 – 7%, No. 16 – 20%, No. 30 – 25%, No. 50 – 20%, No. 100 – 15%, Pan – 10%.

What is your mix and list out what you can do to make a durable mix that is economically competitive? How would you adjust the workability of the mix?

Solutions

Expert Solution

Ans) Let the total volume of trial mix be 1 cubic yard (27 ft^3) then according to ACI 211.1.8 , table 6.3.1 , slump required for slab is 1 to 3 in .

ASTM C33 #57 stone has a nominal size between 1 to 0.19 in.So, according to Table 6.3.3 for 3 in slump and nominal aggregate size of 1 in , amount of water required per cubic yard of concrete is 325 lb/cy

=> Amount of water = 325 lb/ cubic yard concrete

According to Table 6.3.3 approximate air content in concret for 1 in aggregate = 1.5%

According to ACI 318, Design compressive strength is :

fcr = f'c + 1200

f'c is specified compressive strength

=> fcr = 3000 + 1200 = 4200 psi

=> fcr = 4200 psi

Now according to Table 6.3.4 (a) , for compressive strength of 4200 psi , water cement ratio is 0.55

Hence, amount of cement = 325/ 0.55 = 590.9 lb/cy

Sieve number % Retained Cumulative % retained
No.4 3 3
No.8 7 10
No.16 20 30
No.30 25 55
No.50 20 75
No.100 15 90

Fineness modulus, FM = Sum of cumulative retained /100 = (3 + 10 + 30 + 55 + 75 + 90) / 100 = 2.63

Now, according to table 6.3.6 for nominal aggregate size of 1 in and fineness modulus of 2.63, volume of coarse aggregate is 0.69 ft^3 or 18.63 cy

=> Amount of coarse aggregate = Dry rodded density x volume

Assuming dry rodded density of coarse aggregate as 95 lb/ft^3

=> Amount of coarse aggregate = 95 x 18.63 = 1769.85 lb

Volume of fine aggregate = Total volume of concrete - Volume of water,cement,coarse aggregate and air

=> Fine aggregate volume = 27 - [(325/62.4) + (590.9 / 3.15 x 62.4) + (1769.85/ 2.6 x 62.4) + 0.015(27)]

=> Fine aggregate volume = 27 - 19.53 = 7.47 ft^3

=> Amount of fine aggregate = Volume x Specific gravity x Water density = 7.47 x 2.6 x 62.4 = 1212

Material Amount (lb)
Cement 325
Water 590.9
Coarse aggregate 1769.85
Fine aggregate 1212

To make durable mix that is economically competitive, follow the give steps :

1) Insure proper compaction is done

2) Use of admixtures to reduce water demand and improve workability

3) Use of lumps free durable cement

4) Choosing the best estimate of aggregate size to be used in concrete

To adjust workability of the mix :

1) Choose a w/c ratio wisely. Higher the w/c ratio higher will be the workability but lesser will be strength

2) Using of admixtures like superplastizers , retarders etc   


Related Solutions

Design the concrete mix according to the following conditions: Design Environment Pavement slab, Bozeman, Montana (cold...
Design the concrete mix according to the following conditions: Design Environment Pavement slab, Bozeman, Montana (cold climate) Required design strength = 3000 psi Slab thickness = 12 in Statistical data indicate a standard deviation of compressive strength of 250 psi is expected (more than 30 samples) Only air entrainer is allowed. Available materials Air entrainer: Manufacture specification is 0.15 fl oz/1% air/100lb cement Coarse aggregate: 2in. nominal maximum size, crushed stone Bulk oven dry specific gravity = 2.573, absorption =...
What will you propose for a concrete mix design to be used in constructing a bridge...
What will you propose for a concrete mix design to be used in constructing a bridge pier during a cold winter month. The bridge is designed to be constructed on a site where sulfate attack on the concrete is a problem. In this project, high cost is not allowed and the concrete’s cost must be priority without lowering quality.
Three different anchor bolts were installed in a 12" -2500 PSI concrete strength slab. The bolts...
Three different anchor bolts were installed in a 12" -2500 PSI concrete strength slab. The bolts were all 1/2 diameter with 6" embedment depth. The types were mechanical, epoxy, and cast in place during original pour. which anchor bolt would you predict would take the greatest force to pull out from the slab and why
Design a concrete mix for the superstructure of a building using DoE mix design method requiring...
Design a concrete mix for the superstructure of a building using DoE mix design method requiring a characteristic strength of 40MPa at 28days and a slump of 30-60mm. The materials available are ordinary Portland cement, and uncrushed fine and coarse aggregates of specific gravity of 2.65. The maximum nominal size of coarse aggregate is 10mm and fine aggregate confirms to the grading zone III. Neglect the effect of standard deviation and other factors.
  A concrete mix is designed to withstand 3000 pounds per square inch​ (psi) of pressure. The...
  A concrete mix is designed to withstand 3000 pounds per square inch​ (psi) of pressure. The following data represent the strength of nine randomly selected casts​ (in psi). ​3970 4090 3000 2950 3840 4090 4040 3490 Compute the​ mean, median and mode strength of the concrete​ (in psi).
A concrete mix is designed to withstand 3000 pounds per square inch​ (psi) of pressure. The...
A concrete mix is designed to withstand 3000 pounds per square inch​ (psi) of pressure. The following data represent the strength of nine randomly selected casts​ (in psi). 3960​, 4090​, 3200​, 3000​, 2950​, 3830​, 4090​, 4040​, 3780    Compute the​ mean, median and mode strength of the concrete​ (in psi). Compute the mean strength of the concrete. Select the correct choice below​ and, if​ necessary, fill in the answer box to complete your choice. A.The mean strength of the concrete...
concrete C25 mix design lab report
concrete C25 mix design lab report
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in...
Design a concrete mix for reinforced concrete beams of a structure. The structure is located in a locality wherein water has excess of chlorides in it. Required average compressive strength of concrete has been determined to be 4700 psi. Beams have cross-section of 9 in. x 21 in. reinforced with 4 # 6 bars. Reinforcement has a concrete cover of 1.25 in. and there is a clear space of 1.0 in. between form surface and steel bars. Fine aggregate has...
I mention everything in detail (Concrete mix design) INTRODUCTION TO REINFORCED CONCRETE
I mention everything in detail (Concrete mix design) INTRODUCTION TO REINFORCED CONCRETE
Design a concrete mixture that has a 28 day compressive strength of 4000 psi and a...
Design a concrete mixture that has a 28 day compressive strength of 4000 psi and a maximum size aggregate of 0.75 in. The concrete would be placed in a column exposed to freezing and thawing and will be in contact with a soil that has a sulfate content of 0.3%. Step 1: Assemble information from specifications and local materials Cement: Use any type and assume a specific gravity of 3.15 Coarse Aggregate: Bulk Specific Gravity (BSG) – 2.65 Absorption Capacity...
ADVERTISEMENT
ADVERTISEMENT
ADVERTISEMENT